[RE-wrenches] Low output

Jerry Shafer jerrysgarage01 at gmail.com
Wed Jun 20 11:49:46 EDT 2018


Bill
Leave the PV off for a day or so it drop the battery voltage down, yes way
down to say 1 or 2 above your LVD, then at mid day turn on the PV at this
point your system should go WOT and you should see the output expected. The
biggest reason why you are not seeing the amps is demand and the range of a
24 volt system is pretty tight, because you are "off grid" the pv system is
responce based and without demand there is just the float output, whereas
connected to the grid you can always max out power. As a seperate note you
can push FLA L-16 to 31 volts adjusting for temps
Jerry

On Tue, Jun 19, 2018, 9:51 PM frenergy <frenergy at psln.com> wrote:

> Off-gridders,
>
>              Small 24 volt off-grid install.....new installation, 3, 285
> watt PVs in series, 4, L-16's in series, Midnight "Kid" CC.  Problem: I
> cannot get more than about 200 watts (8-9 amps battery side) out of the
> Kid display in full noon sun, clean PVs. Should be 700 watts plus and
> about 28 amps.  Bulk/Absorb set at 29V, battery voltage at ~25 V (pulled
> down with a heat gun).  I changed that Kid out for another new one> Same
> issue!  I disconnected the PV wires where they land in the Kid and got
> 9.3 amps short circuit, 105 volts oc  Called Midnight tech support but
> we couldn't come up with a good solution.  Ideas?
>
> Thx,
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
>
> ---
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180620/1d45275a/attachment.htm>


More information about the RE-Wrenches mailing list