[RE-wrenches] Xfmr's job?

Drake drake.chamberlin at redwoodalliance.org
Thu May 31 08:09:55 EDT 2018


That is interesting about Magnum: Tech support 
told me that the 4024PAE  was two separate 2000 W 
inverters. We had problems with a microwave shutting the system down.

Do you find you have good reliability with Magnum products?

Drake


At 03:53 PM 5/30/2018, you wrote:
>HI Dave and everyone, Its interesting because 
>there is a great deal of difference between 
>OEM’s. Outback says 4kw at 120v for 8kw 
>radian. ( tech support) Magnum says 27 amps at 
>120v, 16.7 amps at 240 for MS4024PAE ( from the 
>manual) Schneider  says 4200 watts at 120v on 
>XW-6848 ( from the manual) Also I know that the 
>Magnum allows you to charge with just 120v and I 
>think the XW is the same, OB you have to have 
>240v. Cheers jay > On May 30, 2018, at 7:52 AM, 
>Dave Angelini Offgrid Solar 
><offgridsolar at sti.net> wrote: > > The 8kw radian 
>still has to have balance! You can't expect it 
>to supply > 8kw  @ 120vac. It can supply 8kw  @ 
>240 vac. > > >> Does each of the 4 kW 240 volt 
>inverters have a maximum on the 120-volt >> 
>power it can supply?  for example, can it supply 
>70% of the 4 kW on 120 >> -volts? >> This 
>example would leave 5.6 kW of 120-volt? >> >> On 
>Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 >> 
><jerrysgarage01 at gmail.com> >> wrote: >> >>> The 
>Radian has 2, 4k, 240 volt inverters, so its 
>different but the way >>> the >>> computer works 
>it makes the same from the load side of 
>things >>> Jerry >>> >>> >>> >>> Sent from my 
>Verizon, Samsung Galaxy smartphone >>> >>> >>> 
>-------- Original message -------- >>> From: 
>frenergy <frenergy at psln.com> >>> Date: 5/29/18 
>5:51 PM (GMT-10:00) >>> To: 
>re-wrenches at lists.re-wrenches.org >>> Subject: 
>[RE-wrenches] Xfmr's job? >>> >>> Hey 
>folks, >>> >>>            Outback FP2 with Xfrmr 
>shifts power to "other" leg if that >>> leg 
>needs more than the one FX can provide, 
>right?  Say, you need 5.5 KW >>> on leg 1, the 
>Xfrmr pulls some power from the leg 2 (inverter) 
>to >>> support that 5.5KW load on leg 1. >>> >>> 
>My question (assuming above is accurate) is does 
>the 8048 Radian do the >>> same? >>> >>> 
>Thanks, >>> >>> Bill >>> >>> Feather River Solar 
>Electric >>> Bill Battagin, Owner >>> 4291 
>Nelson St. >>> Taylorsville, CA 95983 >>> 
>530.284.7849 >>> CA Lic 874049 >>> 
>www.frenergy.net >>> >>> >>> --- 
>_______________________________________________ 
>List sponsored by Redwood Alliance List Address: 
>RE-wrenches at lists.re-wrenches.org Change 
>listserver email address & settings: 
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>List-Archive: 
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>List rules & etiquette: 
>www.re-wrenches.org/etiquette.htm Check out or 
>update participant bios: www.members.re-wrenches.org



More information about the RE-Wrenches mailing list