[RE-wrenches] Xfmr's job?

jay jay.peltz at gmail.com
Wed May 30 15:53:04 EDT 2018


HI Dave and everyone,

Its interesting because there is a great deal of difference between OEM’s.

Outback says 4kw at 120v for 8kw radian. ( tech support)

Magnum says 27 amps at 120v, 16.7 amps at 240 for MS4024PAE ( from the manual)

Schneider  says 4200 watts at 120v on XW-6848 ( from the manual)

Also I know that the Magnum allows you to charge with just 120v and I think the XW is the same, OB 
you have to have 240v.

Cheers

jay





> On May 30, 2018, at 7:52 AM, Dave Angelini Offgrid Solar <offgridsolar at sti.net> wrote:
> 
> The 8kw radian still has to have balance! You can't expect it to supply
> 8kw  @ 120vac. It can supply 8kw  @ 240 vac.
> 
> 
>> Does each of the 4 kW 240 volt inverters have a maximum on the 120-volt
>> power it can supply?  for example, can it supply 70% of the 4 kW on 120
>> -volts?
>> This example would leave 5.6 kW of 120-volt?
>> 
>> On Tue, May 29, 2018 at 11:09 PM, jerrysgarage01
>> <jerrysgarage01 at gmail.com>
>> wrote:
>> 
>>> The Radian has 2, 4k, 240 volt inverters, so its different but the way
>>> the
>>> computer works it makes the same from the load side of things
>>> Jerry
>>> 
>>> 
>>> 
>>> Sent from my Verizon, Samsung Galaxy smartphone
>>> 
>>> 
>>> -------- Original message --------
>>> From: frenergy <frenergy at psln.com>
>>> Date: 5/29/18 5:51 PM (GMT-10:00)
>>> To: re-wrenches at lists.re-wrenches.org
>>> Subject: [RE-wrenches] Xfmr's job?
>>> 
>>> Hey folks,
>>> 
>>>            Outback FP2 with Xfrmr shifts power to "other" leg if that
>>> leg needs more than the one FX can provide, right?  Say, you need 5.5 KW
>>> on leg 1, the Xfrmr pulls some power from the leg 2 (inverter) to
>>> support that 5.5KW load on leg 1.
>>> 
>>> My question (assuming above is accurate) is does the 8048 Radian do the
>>> same?
>>> 
>>> Thanks,
>>> 
>>> Bill
>>> 
>>> Feather River Solar Electric
>>> Bill Battagin, Owner
>>> 4291 Nelson St.
>>> Taylorsville, CA 95983
>>> 530.284.7849
>>> CA Lic 874049
>>> www.frenergy.net
>>> 
>>> 
>>> ---


More information about the RE-Wrenches mailing list