[RE-wrenches] old sanyos failing Iso test
Jerry Shafer
jerrysgarage01 at gmail.com
Sun May 13 14:51:20 EDT 2018
Kirk
I dont know if you know this but Panisonic will warranty the old Sanyos,
just got this from a rep last week.the issue you are having may be due to
the failing of the back sheet under the frame edge.
Jerry
On Sun, May 13, 2018, 6:04 AM Kirk Herander <vtsolar at icloud.com> wrote:
> I now have two systems with older Sanyos(Panasonic), circa 2004, which
> consistently fail the inverter (Solaredge) startup Insolation test in wet
> weather. Usually 200 – 550 kohms, just below the inverters 600k limit.
> Confirmed by my meggering. I discovered this after convincing the owners to
> upgrade the inverters from old SMA’s which don’t test for it. Anyone else
> see this issue in older panels, in particular Sanyos?
>
>
>
> *Kirk Herander*
>
> *Owner|Principal, VT Solar, LLC *
>
> *Celebrating our 27th Anniversary 1991-2018*
>
> *www.vermontsolarnow.com <http://www.vermontsolarnow.com>*
>
> dba Vermont Solar Engineering
>
> NABCEPTM 2003 Inaugural Certificant
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>