[RE-wrenches] old sanyos failing Iso test
Kirk Herander
vtsolar at icloud.com
Sun May 13 11:21:57 EDT 2018
I now have two systems with older Sanyos(Panasonic), circa 2004, which
consistently fail the inverter (Solaredge) startup Insolation test in wet
weather. Usually 200 - 550 kohms, just below the inverters 600k limit.
Confirmed by my meggering. I discovered this after convincing the owners to
upgrade the inverters from old SMA's which don't test for it. Anyone else
see this issue in older panels, in particular Sanyos?
Kirk Herander
Owner|Principal, VT Solar, LLC