[RE-wrenches] Fullriver Battery meltdown
Steve Higgins
steve at surrette.com
Thu May 10 19:47:07 EDT 2018
Hey Guys, just throwing this out there... I know these weren't mine (Rolls)
but I've seen this happen and in 99% of the cases it's excessive heat.
AGM's typically don't enter thermal runaway, like the older 90's and 00's
Gels did...
I asked earlier about the temp sensors, on these they should be mounted
about 1/2 way down on one of the long sides. The side mount sensors are
best as the temp variance between the side and the top terminal can be as
much as 20 degrees... this is going to cause over charging, and thus too
much heat every time.
Here is a FLIR shot of a battery bank while under charge:
You can see the difference in the temps between the posts, and the side of
the battery bank.
Most battery companies will tell you that side mounted sensors, in the
warmest location of the bank is where you want your BTS.
Another issue with these, for for that matter any VRLA battery is gassing.
When they are charging, even in a 55F room they will get warm, typically in
Bulk/Absorb about 20-25F higher, in hot (Above 77F) environment this often
can be as high as 90-120F. when this happens the valves on the battery
"burp". If you have tie down straps going across the top of the battery
this will restrict the valve from opening, thus ballooning out the chassis
or jar. In this case it's better to lay them on their long, or short
sides, than to let them stand vertically.
AGM's and GEL's will gas, especially when heated above 77F, when you are
charging is when most of that heat is going to build up.
Last but no least spacing between the batteries is important, it's a good
idea to have 1-2 inches of space between them at all times.
Had a case recently that I did a site visit on battery bank on a boat in
Florida.
All the batteries (8) boiled out and cooked... same type of damage. When
I got to the site all the batteries had severe heating damage to the
plates.
Upon inspection of the programming I found that the Float set point was set
to the Absorb Voltage, and the BTS has been eaten by a animal of some
sort... When that occurred it shorted the BTS on the inverter making the
inverter think that the battery temp was -2C... this caused the Inverter to
charge at over 31 volts for 3 months before the owner found the battery and
had cooked...
Just saying... when this happens it's often a battery temp issue, and not a
battery issue... and yes, I would have said that even if I didn't work for
a battery manufacture.
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020 m +1.206.790.5840
f +1.902.597.8447 e steve at surrette.com
<#UNIQUE_ID_SafeHtmlFilter_> <http://www.facebook.com/RollsBattery>
<http://www.facebook.com/RollsBattery> <http://www.twitter.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------
On Thu, May 10, 2018 at 4:18 PM, Michael Morningstar <
mjmorningstar at gmail.com> wrote:
> The picture shows a group of new Fullriver batteries destined for a
> different site, and the ruined Crown’s I had just pulled out. They are
> sitting in the back of my truck. Batteries were in a basement that stays
> 55F year round. Temp sensors for both the Magnum inverter and Midnite
> Classic 150. Small array(600 watts). 2/0 cables. Absorb time 1.5 hours.
> Factory recommended charging parameters. Tight connections. My first
> thermal runaway after hundreds and hundreds of battery bank installs too.
> My local distributor has been pushing Crowns and their great warranty so I
> reluctantly gave them a shot. Lead acids and AGMs. I’m not impressed with
> either. Nor their warranty process.
>
> I
>
> On May 10, 2018, at 3:49 PM, Rick Brown <rick@
> solshineenergyalternatives.com> wrote:
>
> I’m inclined to agree with Maverick. Mixing old and new batteries is not
> recommended. Differing internal resistance coupled with potentially extreme
> temps can lead to thermal runaway.
>
> rick brown
> SolShine Energy Alternatives, LLC
> Electrical & Solar Contracting Services
> www.SolShineEnergyAlternatives.com
> <http://www.solshineenergyalternatives.com/>
> Check, Virginia 24072
> 540.808.9502
>
> VA Class A Contractor Lic# 2705147660
> VA Master Electrician Lic# 2710062762
> VA Alternative Energy Systems Installer
> NABCEP Certified PV Installation Professional 110112-21
>
> On May 10, 2018, at 6:02 PM, "maverick at mavericksolar.com" <
> maverick at mavericksolar.com> wrote:
>
> Looks like a mix of old and new Batteries in a cabinet too small to drain
> excessive heat gain. Was the cabinet shaded? Or exposed to direct sun? Temp
> sensor on charging source?
> What size interconnect cables were used?
> Was it a bus system?
> Absorb with End Amps was turned on?
>
> Sent from my iPhone
>
> On May 10, 2018, at 4:41 PM, Michael Morningstar <mjmorningstar at gmail.com>
> wrote:
>
> <image1.jpeg>
> One year old. Well looked after system.
> On May 10, 2018, at 1:42 PM, Starlight Solar Power Systems <
> larry at starlightsolar.com> wrote:
>
> Wrenches,
>
> Attached is a photo of my first thermal runaway event after 17 years and
> thousands of battery systems installed. These were in an RV. I checked
> every charge source and all are within specified charging parameters. No
> cause found. The owner is a single elderly lady that uses very little power
> in her RV and spend most of the time on shore power. She reported that the
> batteries were dead when she unplugged from shore power. This was i the
> 23rd month after installation.
>
> After I reported this to my Fullriver distributor, they told me that
> another set of DC400-6 had melted down just 1 month earlier and that they
> had fused together just like these. That is extreme heat. It is too
> peculiar to know of two similar events. This meltdown happened within the 2
> year warranty period but my customer could not come back to us for another
> 3 months beyond the warranty period. Fullriver would not allow anything
> towards replacement do to the reporting date being grater than 24 months.
>
> I would like to know has anyone else had a similar failure with Rolls or
> Fullriver AGM batteries, specifically L16 size.
>
> Thank you,
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
> <IMG_0627.jpeg>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180510/1726e341/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 209307 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180510/1726e341/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 218576 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180510/1726e341/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 507473 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180510/1726e341/attachment-0002.png>
More information about the RE-Wrenches
mailing list