But if you are net metering, doesn’t your utility have to replace the kWh meter anyway?

Here and in NY, it is common practice for an installer to pull a meter where a supply side connection is to be made.

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana
Sent: Thursday, February 22, 2018 6:55 PM
To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] B3 Bypass breaker

 

Per my Master AC electrician, you do not have to arrange for a meter pull with the utility. That to me is one less piece of brain damage to deal with.

I have not checked out the cost of a back fed breaker VS this item.

 

----------------------------------------------------------------------------

Dana Orzel                              Great Solar Works, Inc. 

C - 208.721.7003                       dana at solarwork.com <mailto:dana at solarwork.com> 

Idaho Contractor - # 028765         Idaho PV # 028374

NABCEP # 051112-136                       www.solarwork.biz <http://www.solarwork.biz> 

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Lorenzo Ortiz
Sent: Thursday, February 22, 2018 1:10 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> >
Subject: Re: [RE-wrenches] B3 Bypass breaker

 

How is this different/better/less expensive than just doing a supply side tap using insulated connectors (NSI's)?

 

>From what I can tell, it only works on panels that are fed with wire conductors from the meter not hard bussing, so why not just tap it?

 

 

 

On Thu, Feb 22, 2018 at 7:20 AM, Sam Haraldson <sam at onsiteenergyinc.com <mailto:sam at onsiteenergyinc.com> > wrote:

On Wed, Feb 21, 2018 at 8:00 AM, Dana <dana at solarwork.com <mailto:dana at solarwork.com> > wrote:

Has anyone used the B3 buss-bar bypass breaker setup yet?  <http://www.qfe002.com> www.qfe002.com

 

At SPI this year I spoke with one of their reps briefly and they indicated that after many years of trying to get the product ready it was finally going to be in production.  I have researched it no further than that however.  

 

- Sam

 

 

-- 

Sam Haraldson, Installation Manager
Office: 406.551.6135 <tel:(406)%20551-6135> 
sam at onsiteenergyinc.com <mailto:sam at onsiteenergyinc.com> 
onsiteenergyinc.com <http://onsiteenergyinc.com>  

  <http://onsiteenergyinc.com/assets/img/main/onsite-energy.png> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 





 

-- 

Lorenzo Ortiz   Commercial Design/Support

 

    lorenzo at cal-solar.com <mailto:lorenzo at cal-solar.com>   (530) 274-3671

    <https://docs.google.com/uc?export=download&id=0B6l5VcsZgAv3TXRfSkhpZUNaczQ&revid=0B6l5VcsZgAv3djFpMk9EQUdEdmg1K0hFdHBNZVlTZ3RZdW5VPQ> 

 


 <http://californiasolarco.com/referral-program/> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180222/362cc1d3/attachment.htm>


More information about the RE-Wrenches mailing list