[RE-wrenches] Adding generators to PV systems

Aaron Mandelkorn reosolar at gmail.com
Fri Jan 12 18:06:17 EST 2018


We do these all the time.  Relocation of the pv input from the load center
to the utility side of the generator transfer switch has always been our
solution.

Aaron Mandelkorn
President / Founder
Renewable Energy Outfitters
www.reosolar.com
Off Grid Depot
www.offgridnow.com
970-596-3744



On Jan 12, 2018 4:00 PM, "Jerry Shafer" <jerrysgarage01 at gmail.com> wrote:

> Wayne
> We will not connect a grid tie inverter down stream of a gen-set, you
> don't want the inverter attempting to connect, when it comes right down to
> it, Why would you want to it would be a very small micro grid that if and
> when the demand is less then the inverter output would be then the gen-set
> would produce no power, volts yes amps no, then the volts climb the
> inverter discos and bam the genny has to make it all up. We have 8 k to 250
> k gennys and PV systems attached all are upstream or in switches to turn
> them off.
> Jerry
>
> On Thu, Jan 11, 2018 at 3:54 PM, Wayne Irwin <PureEnergySolar at hotmail.com>
> wrote:
>
>> Hello All,
>>
>>
>> We have several customers adding generators to their homes on which we
>> have previously installed PV systems.
>>
>> Historically most generators didn't produce a clean enough 60Hz sinewave
>> to get the inverters to feed back.
>>
>> However, with the generator technology improving and the introduction of
>> inverter generators, I'm concerned that if the inverters feed back to the
>> generator it will smoke the stator.
>>
>>
>> I'm wondering if any of you have any experience/issues?  If so, what
>> solutions or recommendations do you have?
>>
>>
>> Thanks,
>>
>>
>>
>> Wayne Irwin,
>> President
>> License #CVC56695
>> State Licensed Solar Contractor
>> Pure Energy Solar International Inc.
>> Wayne at PureEnergySolar.com <PureEnergySolar at hotmail.com>
>> <http://pureenergysolar.net/>http://PureEnergySolar.com
>> http://SolarChargingStation.net <https://solarchargingstation.net>
>> 352 377-6527 <(352)%20377-6527> Office
>> 352 336-3299 <(352)%20336-3299> Fax
>>
>>
>> The Sun Is Always Shining!
>>
>> The content of this message is Pure Energy Solar Confidential. If you are
>> not the intended recipient and have received this message in error, any use
>> or distribution is prohibited. Please notify me immediately by reply e-mail
>> and delete this message from your computer system. Thank you.
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenches at lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180112/5764dfc9/attachment.htm>


More information about the RE-Wrenches mailing list