JERRY:

I always specify separate breakers per string (175A or 250A, depending 
on string ampacity) mounted as close to the battery bank as possible. 
And I require that if I am to be engaged for maintenance (planned or 
unplanned) after commissioning. Shunt-trip breakers facilitate meeting 
Rapid Shutdown requirements.

Separate string breakers make battery maintenance and trouble shooting 
so much easier and well worth the first cost investment. Especially so 
when you have bad or weak cells/batteries, uneven string 
discharge/charge current, and need to isolate the culprit(s).

If I have a maintenance arrangement with the customer, individual string 
breakers allow me to quickly/safely perform string/battery SOH (state of 
Health) testing with an internal resistance tester and/or a load test on 
individual batteries without removing wiring/busbars/etc.

Regards,

Gary Willett PE
Icarus Engineering / Solar Services LLC

On 12/1/17 7:46 PM, Jerry Shafer wrote:
> More then two banks require fusing or breakers, its best on anything amount
> including one all to be located at or near the battery.
> Jerry
>
> On Dec 1, 2017 10:03 AM, "jay" <jay.peltz at gmail.com> wrote:
>
>> HI All,
>>
>> I’m wondering if anyone has a good source for battery buss bar stock.
>> Either pre made ones or stock I can use to make myself.
>>
>> It would be for larger Rolls GEL 2v in this case but other battery
>> sizes/types as well.
>>
>> thanks
>>
>> jay
>>
>> peltz power
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>



More information about the RE-Wrenches mailing list