May I ask is the delay to comply with NEC 702? Has the grid to go down and
for long enough for the transfer switch to change over from grid to
off-grid?
On Mon, Nov 20, 2017 at 2:40 PM, Dave Tedeyan <dtedeyan at taitem.com> wrote:
> Gary,
> Sorry for the delay. You had asked me about the Enphase/Sonnen solution,
> copied below.
>
> Since this is a grid tied battery backup situation, the only brute OFF
> situations would be
> in a grid outage. Once the batteries are charged, then the Sonnen continues
> to sell extra
> PV to the grid. And in the case of a power outage, the Sonnen is actually a
> little slow in
> transitioning. It takes around 10 seconds (if I remember correctly) for the
> Sonnen to start
> powering the backed up loads. So no matter what you have for the AC coupled
> PV, you
> will have a small gap in power during an outage.
>
> I hope this answered your question... If not, I'll try to respond quicker
> next time.
> Cheers,
> Dave
>
>
> > DAVE:
> >
> > How does the brute force OFF transitions of the 8K of Enphase AC-coupled
> > micro-inverters affect the AC loads being served by the Sonnen? Are
> > there any noticeable/measurable glitches in the Sonnen's distributed AC?
> >
> > I am assuming the Enphase ON transitions are more graceful because of
> > the UL1741 prove-in period and the individual ramp-up of the individual
> > microinverters.
> >
> > Regards,
> >
> > Gary Willett PE
> > Icarus Engineering & Solar Services LLC
>
>
> *--*
>
>
> *Dave Tedeyan*
> *Project Engineer*
>
> *Taitem Engineering, PC*
> 10 Verizon Lane, Lansing, NY 14882
> Voice: (607) 930-3481 x6
> www.taitem.com
>
> On Mon, Nov 13, 2017 at 10:52 AM, Drake <
> drake.chamberlin at redwoodalliance.org> wrote:
>
> > Hi Nick,
> >
> > Please send me your information. Currently I am finishing up an Enphase
> > M-250, AC coupled system that is designed to taper charge batteries by
> > dropping out groups of inverters based on battery voltage.
> >
> > Thanks,
> >
> > Drake
> >
> > Drake Chamberlin
> > Athens Electric LLC
> > OH License 44810
> > CO License 3773
> > NABCEP Certified Solar PV
> > 740-448-7328
> >
> >
> >
> > At 11:58 PM 11/11/2017, you wrote:
> >
> >> Hi Wrenches,
> >>
> >>
> >> We now have the ability to provide frequency based power curtailment.
> If
> >> you are AC Coupling with a battery-based inverter that can fluctuate
> >> frequency to regulate charge on the battery, then we can ramp our
> output up
> >> and down to regulate the charge more evenly.
> >>
> >>
> >> If you have an AC Coupled system using Enphase microinverters, reach out
> >> to me and I will set your company up with a grid profile that can
> provide
> >> this option. Once your company has been granted access to this profile,
> >> you can update the profile using either our Installer Toolkit (ITK) app
> or
> >> Enlighten.
> >>
> >>
> >> Cordially,
> >>
> >> Nick Soleil
> >>
> >> Enphase Energy | Product Manager, Envoy and IQ Accessories
> >>
> >>
> >> (707) 763-4784 x7267 // office
> >>
> >> (707) 321-2937 // cell
> >>
> >> [Enphase_esig_logo6.jpg]<https://enphase.com/>
> >>
> >>
> >> Energy Evolved<http://enphase.com>™
> >>
> >> Powering What’s Next™ | The Enphase Energy Management System<
> >> http://ow.ly/HbVS3>
> >>
> >>
> >> NABCEP Certified Solar PV Installer #03262011-300
> >>
> >> California C10 Licensed Electrician #986315
> >>
> >> Texas Master Electrician #284451
> >>
> >>
> >>
> >>
> >> ________________________________
> >> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf
> >> of Gary Willett <Gary at IcarusSolarServices.com>
> >> Sent: Saturday, November 11, 2017 3:34 PM
> >> To: re-wrenches at lists.re-wrenches.org
> >> Subject: Re: [RE-wrenches] Battery Backup for Older Enphase Systems
> >>
> >> DAVE:
> >>
> >> How does the brute force OFF transitions of the 8K of Enphase AC-coupled
> >> micro-inverters affect the AC loads being served by the Sonnen? Are
> >> there any noticeable/measurable glitches in the Sonnen's distributed AC?
> >>
> >> I am assuming the Enphase ON transitions are more graceful because of
> >> the UL1741 prove-in period and the individual ramp-up of the individual
> >> microinverters.
> >>
> >> Regards,
> >>
> >> Gary Willett PE
> >> Icarus Engineering & Solar Services LLC
> >>
> >>
> >> On 11/9/17 2:28 PM, Dave Tedeyan wrote:
> >> > You could go with a Sonnen. That is meant to be AC coupled, and its a
> >> very
> >> > simple install.
> >> > Nice piece of equipment, but its expensive. We just installed one that
> >> has
> >> > right around 8kw of Enphase M215 inverter output. So far, no issues.
> >> >
> >> > Cheers,
> >> > Dave
> >> >
> >> >
> >> > *--*
> >> >
> >> >
> >> > *Dave Tedeyan*
> >> > *Project Engineer*
> >> >
> >> > *Taitem Engineering, PC*
> >> > 10 Verizon Lane, Lansing, NY 14882
> >> > Voice: (607) 930-3481 x6
> >> > www.taitem.com<http://www.taitem.com>
> >> >
> >> > On Thu, Nov 9, 2017 at 2:07 PM, John <john at gosolar.co.nz> wrote:
> >> >
> >> >> We did one a few months ago using Outback VFX3024e, 1000 a/h battery
> >> bank
> >> >> - basically an Off-Grid system but tied into the switchboard, with
> >> customer
> >> >> nominated circuits dedicated to the Off-Grid system. The grid is
> >> acting
> >> >> like the backup generator via a relay.
> >> >>
> >> >> The only little hiccup was that when the *generator* was called on,
> the
> >> >> Off-Grid system had to sync in with the real Grid, it was not
> >> immediate.
> >> >>
> >> >> Apart from that - seems to work O.K. John,
> >> GoSolar
> >> >> Ltd, Christchurch, N.Z.
> >> >>
> >> >> ++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
> >> >> ++++++++++++++++++++++++++++++++++++++++++++++++
> >> >>
> >> >> -----Original Message-----
> >> >> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> >> On
> >> >> Behalf Of Matt Sherald
> >> >> Sent: Friday, 10 November 2017 3:43 a.m.
> >> >> To: RE-wrenches
> >> >> Subject: [RE-wrenches] Battery Backup for Older Enphase Systems
> >> >>
> >> >> I'd appreciate some ideas as to what backup system designs work well
> >> with
> >> >> the older Enhase equipment (M250/215 era).
> >> >>
> >> >> I've tried this at home with a XW4024, but the frequency rise causes
> >> the
> >> >> lights to flicker and it is awfully unpleasant.
> >> >>
> >> >> A customer of mine has asked about backup to go with an array that
> uses
> >> >> M250s and this prompted me to write.
> >> >>
> >> >> Thanks in advance!
> >> >>
> >> >> -Matt
> >> >>
> >> >> --
> >> >> Matt Sherald
> >> >> PIMBY Energy, LLC
> >> >> NABCEP Certified Solar PV Installer®
> >> >> 304-704-5943
> >> >>
> >> >> www.getpimby.blogspot.com<http://www.getpimby.blogspot.com>
> >> >> www.getpimby.com<http://www.getpimby.com>
> >> >> _______________________________________________
> >> >> List sponsored by Redwood Alliance
> >> >>
> >> >> List Address: RE-wrenches at lists.re-wrenches.org
> >> >>
> >> >> Change listserver email address & settings:
> >> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >> >>
> >> >> List-Archive: http://www.mail-archive.com/re
> >> -wrenches at lists.re-wrenches.
> >> >> org/maillist.html
> >> >>
> >> >> List rules & etiquette:
> >> >> www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org
> >> /etiquette.htm>
> >> >>
> >> >> Check out or update participant bios:
> >> >> www.members.re-wrenches.org<http://www.members.re-wrenches.org>
> >> >>
> >> >>
> >> >> _______________________________________________
> >> >> List sponsored by Redwood Alliance
> >> >>
> >> >> List Address: RE-wrenches at lists.re-wrenches.org
> >> >>
> >> >> Change listserver email address & settings:
> >> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >> >>
> >> >> List-Archive: http://www.mail-archive.com/re
> >> -wrenches at lists.re-wrenches.
> >> >> org/maillist.html
> >> >>
> >> >> List rules & etiquette:
> >> >> www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org
> >> /etiquette.htm>
> >> >>
> >> >> Check out or update participant bios:
> >> >> www.members.re-wrenches.org<http://www.members.re-wrenches.org>
> >> >>
> >> >>
> >> > _______________________________________________
> >> > List sponsored by Redwood Alliance
> >> >
> >> > List Address: RE-wrenches at lists.re-wrenches.org
> >> >
> >> > Change listserver email address & settings:
> >> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >> >
> >> > List-Archive: http://www.mail-archive.com/re
> >> -wrenches at lists.re-wrenches.org/maillist.html
> >> >
> >> > List rules & etiquette:
> >> > www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org
> >> /etiquette.htm>
> >> >
> >> > Check out or update participant bios:
> >> > www.members.re-wrenches.org<http://www.members.re-wrenches.org>
> >> >
> >> >
> >>
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive: http://www.mail-archive.com/re
> >> -wrenches at lists.re-wrenches.org/maillist.html
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org
> >> /etiquette.htm>
> >>
> >> Check out or update participant bios:
> >> www.members.re-wrenches.org<http://www.members.re-wrenches.org>
> >>
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive: http://www.mail-archive.com/re
> >> -wrenches at lists.re-wrenches.org/maillist.html
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out or update participant bios:
> >> www.members.re-wrenches.org
> >>
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> or
> > g/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list