[RE-wrenches] sizing up equipment ground per NEC 690.45
August Goers
august at luminalt.com
Mon Oct 16 16:54:08 EDT 2017
Hi Wrenches,
Occasionally, we need to up-size the inverter output circuit conductor
sizes (on the inverter AC side) to avoid excessive voltage drop. For
example, we typically use # 10 conductors for a microinverter branch
circuit but occasionally need to up-size to # 8s. A similar scenario might
apply when we have inverters out on on a ground mount array and then have
really long AC runs back to the main service panel location.
Do you think the exception in NEC 690.45 to up-sizing the equipment grounds
applies to these inverter output circuits or not? It is hard to tell
whether 690.45 is meant to only include PV source and PV output circuits:
[image: Inline image 1]
[image: Inline image 2]
Best,
August
*August Goers*
Luminalt Energy Corporation
o: 415.641.4000
www.luminalt.com