[RE-wrenches] 690.47(D)
markf at berkeleysolar.com
markf at berkeleysolar.com
Mon Jan 30 14:00:30 EST 2017
Thanks August,
I have seen the IAEI article from May-June 2015. It seemed to try the line
that if the exisitng electrode is within 6 feet of the building, then that
same electrode is within 6 feet of the "Array".
I guess my plan at this point is to not install the aux. electrode and use
the IAEI article as my justification and see what the inspector is
thinking.
Mark
> Hi Mark,
>
> The current issue of IAEI magazine has an article writing by Bill Brooks
> called "Hot Topics for PV System Installations." In the article, he
> directly addresses 2014 NEC 690.47(D).
>
> Unfortunately I don't see this article posted online, but you might want
> to check it out if you can find it.
>
> My understanding is that the intent of 690.47(D) is to require an
> additional electrode when PV is installed on structures that don't already
> have and electrode system such as a separate building, garage, etc.
>
> August
>
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of markf at berkeleysolar.com
> Sent: Monday, January 30, 2017 10:24 AM
> To: re-wrenches at lists.re-wrenches.org
> Subject: [RE-wrenches] 690.47(D)
>
> Folks,
>
> NEC 2014 is in effect in California. I just pulled a permit for a
> residential system and it had a little stamp that had 690.47(D) circled as
> a requirement.
>
> Anyone worked with AHJ's in California who are now requiring this? I am
> planning to not install the electrode, siting Exception 2 and trying to
> say that the existing electrode next to the build is "next to the array"?
>
> Mark
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
> l
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list