[RE-wrenches] 690.47(D)

August Goers august at luminalt.com
Mon Jan 30 13:47:02 EST 2017


Hi Mark,

The current issue of IAEI magazine has an article writing by Bill Brooks
called "Hot Topics for PV System Installations." In the article, he
directly addresses 2014 NEC 690.47(D).

Unfortunately I don't see this article posted online, but you might want
to check it out if you can find it.

My understanding is that the intent of 690.47(D) is to require an
additional electrode when PV is installed on structures that don't already
have and electrode system such as a separate building, garage, etc.

August

-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of markf at berkeleysolar.com
Sent: Monday, January 30, 2017 10:24 AM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] 690.47(D)

Folks,

NEC 2014 is in effect in California. I just pulled a permit for a
residential system and it had a little stamp that had 690.47(D) circled as
a requirement.

Anyone worked with AHJ's in California who are now requiring this? I am
planning to not install the electrode, siting Exception 2 and trying to
say that the existing electrode next to the build is "next to the array"?

Mark


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
l

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


More information about the RE-Wrenches mailing list