Yes, what current did you use to calculate that voltage drop? How big is
the PV system?

On Aug 16, 2016 11:38 AM, "Chris Mason" <cometenergysystems at gmail.com>
wrote:

> How much of the power produced will be self-consumed, how much will be
> exported?
>
> On Tue, Aug 16, 2016 at 12:16 PM, Howard Arey <scot.arey at solarcentex.com>
> wrote:
>
>> Good day,
>>
>>
>>
>> I have a potential client that has an existing 1,000 foot run from the
>> meter and transformer at the street to the home. This is 4/0 Al and quick
>> calcs show the voltage drop at over 12%. He acknowledges that the wire is
>> undersized to keep voltage at/about 240 volts (I have not measured directly
>> at the street / transformer yet).
>>
>>
>>
>> I know the wire has the necessary ampacity to carry his current service
>> needs and to carry amps from the to-be-suggested solar system.
>>
>>
>>
>> My concern is that the voltage drop will change the 240 volts at the
>> street/transformer/meter to 211ish (or will I see a higher 268’sh voltage
>> at the far house end?) at the house. The inverter will try to synch to this
>> voltage but of course this is outside of typical inverter parameters.
>>
>>
>>
>> So, instead of re-running much large wire, does anybody have experience
>> and comments about potentially using a buck-boots transformer at the home
>> to get us back to 240 volts? This would need to be service entrance sized.
>>
>>
>>
>> *Howard “Scot” Arey*
>>
>> Owner, Solar CenTex
>>
>> 254-300-1228
>>
>> scot.arey at solarcentex.com
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenches at lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installer™
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com <http://www.cometenergysystems.com>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160816/981a0cb5/attachment.htm>


More information about the RE-Wrenches mailing list