How much of the power produced will be self-consumed, how much will be
exported?
On Tue, Aug 16, 2016 at 12:16 PM, Howard Arey <scot.arey at solarcentex.com>
wrote:
> Good day,
>
>
>
> I have a potential client that has an existing 1,000 foot run from the
> meter and transformer at the street to the home. This is 4/0 Al and quick
> calcs show the voltage drop at over 12%. He acknowledges that the wire is
> undersized to keep voltage at/about 240 volts (I have not measured directly
> at the street / transformer yet).
>
>
>
> I know the wire has the necessary ampacity to carry his current service
> needs and to carry amps from the to-be-suggested solar system.
>
>
>
> My concern is that the voltage drop will change the 240 volts at the
> street/transformer/meter to 211ish (or will I see a higher 268’sh voltage
> at the far house end?) at the house. The inverter will try to synch to this
> voltage but of course this is outside of typical inverter parameters.
>
>
>
> So, instead of re-running much large wire, does anybody have experience
> and comments about potentially using a buck-boots transformer at the home
> to get us back to 240 volts? This would need to be service entrance sized.
>
>
>
> *Howard “Scot” Arey*
>
> Owner, Solar CenTex
>
> 254-300-1228
>
> scot.arey at solarcentex.com
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160816/1275e7bc/attachment.htm>
More information about the RE-Wrenches
mailing list