[RE-wrenches] 120% Rule on subpanel or main

Christopher Warfel cwarfel at entech-engineering.com
Thu Mar 31 18:24:17 EDT 2016


What NEC code cycle are you in?  It was changed in 2008. Attached is an 
article from John Wiles in Home Power Code Corner. Chris

On 3/31/2016 1:47 PM, eric at harvesthesun.com wrote:
> Hi Wrenches,
> I know I have seen this somewhere before but can't seem to locate it 
> in the archives. Recently and AHJ rejected our plans because, although 
> we were compliant with the 120% rule applied to the busbar on the 
> existing sub which was our solar PCC, the existing breaker feeding the 
> existing sub (our PCC) exceeded the 120% as it applied to the bus in 
> the main. I was under the impression that the 120% applies to the bus 
> at the PCC and that existing equipment "downstream" or "upstream" of 
> the PCC need not be retrofitted to comply with the 120% rule 
> (conductor ampacity aside).
> Cheers,
> Eric Stikes
> Founding Director & CEO
> Good Sun Solar, A CA non-profit corp.
> www.goodsun.life
> (530)798-3738
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-- 
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160331/190e8841/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: NEC 2008 grid connection CC126.pdf
Type: application/pdf
Size: 364564 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160331/190e8841/attachment.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/x-vcard
Size: 100 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160331/190e8841/attachment.vcf>


More information about the RE-Wrenches mailing list