<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    What NEC code cycle are you in?  It was changed in 2008. Attached is
    an article from John Wiles in Home Power Code Corner. Chris<br>
    <br>
    <div class="moz-cite-prefix">On 3/31/2016 1:47 PM,
      <a class="moz-txt-link-abbreviated" href="mailto:eric@harvesthesun.com">eric@harvesthesun.com</a> wrote:<br>
    </div>
    <blockquote
cite="mid:20160331104713.06812fc9708b5dce7248b6be1695afce.6a947b1f11.mailapi@email13.secureserver.net"
      type="cite">
      <div>Hi Wrenches,</div>
      <div> </div>
      <div>I know I have seen this somewhere before but can't seem to
        locate it in the archives. Recently and AHJ rejected our plans
        because, although we were compliant with the 120% rule applied
        to the busbar on the existing sub which was our solar PCC, the
        existing breaker feeding the existing sub (our PCC) exceeded the
        120% as it applied to the bus in the main. I was under the
        impression that the 120% applies to the bus at the PCC and that
        existing equipment "downstream" or "upstream" of the PCC need
        not be retrofitted to comply with the 120% rule (conductor
        ampacity aside).</div>
      <div> </div>
      <div>Cheers,</div>
      <div> </div>
      <div>Eric Stikes</div>
      <div>Founding Director &amp; CEO</div>
      <div>Good Sun Solar, A CA non-profit corp.</div>
      <div><a class="moz-txt-link-abbreviated" href="http://www.goodsun.life">www.goodsun.life</a></div>
      <div>(530)798-3738</div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978</pre>
  </body>
</html>