Hi Daniel
Is this a new classic with OCP? Or maybe they don't have it anymore?
What it sure sounds like like is a big load on the batteries, it hits faster than the AGS can start, and the caps in the classic are dumping into the super low battery voltage. If this is happening in the AM, guessing with enough light to get the CC alive
If there is a trimetric, you can measure the lowest voltage which should give you some good info. Super low volts might mean a bad battery or too big a load or both.
But I don't believe it's the other way around that the classic is causing any issues with the AGS/inverter
You could always try another CC and see what happens
Jay
Peltz power
> On Oct 26, 2015, at 6:30 PM, Daniel Tittmann <daniel at greenwired.com> wrote:
>
> Hive mind-
> hoping you all can help me solve this mystery issue.
>
> System:
> Magnum double panel with Parallel stacked 2x4448 pae inverters.
> Classic 150 charge controller wired with an NMEPV 50 (din rail) and NMEPV100
> 18 - 245 watt solar modules (6x3). (not over powered)
>
> Issue:
> every morning the 100 amp din rail breaker is tripping. from what I can gather simultaneously the magnum RTR shows the AGS go into error. Re set the breaker and the solar works fine for the rest of the day.
>
> Not 100% sure the AGS has worked (under normal operation) at all other than at commissioning and recent testing.
>
> Of course on site i cant get it to fail.
>
> Tested the AGS by setting start voltage to 48.2 vdc and put the system under load....... voltage drops and generator turned on with no pv-> Batt breaker issue.
>
> last visit, chasing one theory, I re routed the battery + from the mnpv100 directly to the battery + terminal as opposed to the battery + bus bar in the inverter panel still didn't solve the problem.
>
> I cant figure out if it the classic causing the issue or if it is the inverters and the AGS.
>
> Any input would be appreciated.
> Thanks
> Daniel
>
> Daniel Tittmann
> CTO
> Greenwired
> www.greenwired.com
> daniel at greenwired.com
> 707-923-2001 (office)
> 707-206-5088 (Cell)
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20151026/47c4e7d4/attachment.htm>
More information about the RE-Wrenches
mailing list