[RE-wrenches] Classic 150 100 amp utput breaker tripping?????
Daniel Tittmann
daniel at greenwired.com
Mon Oct 26 21:30:22 EDT 2015
Hive mind-
hoping you all can help me solve this mystery issue.
System:
Magnum double panel with Parallel stacked 2x4448 pae inverters.
Classic 150 charge controller wired with an NMEPV 50 (din rail) and
NMEPV100
18 - 245 watt solar modules (6x3). (not over powered)
Issue:
every morning the 100 amp din rail breaker is tripping. from what I can
gather simultaneously the magnum RTR shows the AGS go into error. Re set
the breaker and the solar works fine for the rest of the day.
Not 100% sure the AGS has worked (under normal operation) at all other than
at commissioning and recent testing.
Of course on site i cant get it to fail.
Tested the AGS by setting start voltage to 48.2 vdc and put the system
under load....... voltage drops and generator turned on with no pv-> Batt
breaker issue.
last visit, chasing one theory, I re routed the battery + from the mnpv100
directly to the battery + terminal as opposed to the battery + bus bar in
the inverter panel still didn't solve the problem.
I cant figure out if it the classic causing the issue or if it is the
inverters and the AGS.
Any input would be appreciated.
Thanks
Daniel
Daniel Tittmann
CTO
Greenwired
www.greenwired.com
daniel at greenwired.com
707-923-2001 (office)
707-206-5088 (Cell)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20151026/02dfd9f1/attachment.htm>
More information about the RE-Wrenches
mailing list