[RE-wrenches] AC Coupled with Generator
Drake
drake.chamberlin at redwoodalliance.org
Fri Aug 21 08:27:15 EDT 2015
I'm considering an AC coupled system with Enphase
that would shed inverters a group at a time,
ending up with one still charging until the set point is reached.
At 12:56 AM 8/21/2015, you wrote:
>Hi Folks;
>
>I've done more research on the whole AC coupled
>issue, and one flaw I found with both the Sunny
>Island and the Radian is that they can't really
>do a full 3 stage charge for the batteries in off grid mode.
>They detect that the batteries are full and
>disconnect the AC coupled GT inverters, but this
>is about as subtle as the very early charge
>controllers, and amounts to 1 stage
>charging. This is fine for temporary outages,
>and when the grid comes back, the batteries get
>a good 3 stage charge. But these folks are
>really wanting a design that could be taken off
>grid permanently. Also as you my recall, the
>GT PV system is Enphase, so we can't use the
>more sophisticated controls that SMA offers for the Sunny boys.
>I hate to say it, but I might be back to a
>diversion load with PWM controller. Not
>elegant, but we could get 3 stage charging.
>Every time I look at AC coupled setups, I just
>want to start over with charge controllers.
>
>R.Ray Walters
>CTO, Solarray, Inc
>Nabcep Certified PV Installer,
>Licensed Master Electrician
>Solar Design Engineer
>303 505-8760On 8/17/2015 9:39 PM, Mac Lewis wrote:
>>Hi Ray,
>>
>>With that size grid-tied system, you would want
>>to use a battery based inverter(s) near the (6.7/0.8) 8000W range.
>>
>>The frequency shift of the Sunny Islands will
>>work with kicking out the enphase inverters but
>>you wouldn't get the same output ramping that
>>it would offer if it was a Sunny Boy grid-tied
>>inverter. The Sunny Island can effectively
>>solve your generator backfeeding because there
>>is a reverse current sensor that will
>>disconnect the AC input at whatever level you
>>want, 50 mA is default I think. You may need
>>to give the Sunny Island generator start control for this however.
>>
>>You can read about it here on page 137.
>>
>><http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf>http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf
>>
>>You'll need to give the Sunny Island a digital
>>signal that tell it whether its connected to a
>>generator or a grid as outlined in the manual.
>>
>> This is where the Radian is nice because it has two AC Input terminals.
>>
>>Sounds like an interesting project.
>>
>>Good Luck.
>>
>>
>>
>>
>>On Mon, Aug 17, 2015 at 8:36 PM, Jerry Shafer
>><<mailto:jerrysgarage01 at gmail.com>jerrysgarage01 at gmail.com> wrote:
>>
>>I cant see this working well without some battery based inverter
>>Jerry
>>On Aug 17, 2015 10:10 AM, "Ray Walters"
>><<mailto:ray at solarray.com>ray at solarray.com> wrote:
>>HI Esteemed Wrenches:
>>
>>I am consulting on a system I have never seen,
>>that consists of a 6.7Kw Enphase roof mounted
>>system, and 2 backup generators. Each
>>generator has an automatic 200 amp transfer
>>switch to back up its own 200 amp panel. Both
>>200 amp panels are fed by a 400 amp service from the grid.
>>The Enphase PV backfeeds a subpanel in another
>>building which then is fed by a 2 pole 60 amp
>>breaker in one of the 200 amp panels.
>>Currently they are having issues with the
>>generators kicking out because of the Enphase
>>inverters. That part I understand: you can't
>>backfeed a generator, or its voltage regulation freaks out.
>>
>>Now we get to the fun part: they want to create
>>a third critical load subpanel with loads
>>selected from both 200 amp panels to be powered by batteries and an inverter.
>>I am considering the Sunny Island since it
>>makes the most sense with its ability to signal
>>the Enphase inverters to shut off when the
>>batteries are full. I also see this as a
>>partial solution to the generator issue, since
>>normally the Enphase will be connected to the
>>output side of the Sunny Island. However, when
>>the generator is used to charge, we will be
>>back to directly coupling the generator output to the Enphase.
>>
>>Here are some possible solutions I'm considering:
>>1) Use a separate charger for the generator so
>>that it will only feed DC to the batteries, and not be AC coupled.
>>2) convert the PV back to DC with charge
>>controllers, but that would involve ditching
>>and adding another conduit run between buildings.
>>3) Put the Enphase PV on a relay that would
>>disconnect the PV when charging with the generator.
>>4) Something I haven't thought of that one of
>>you clever folks can suggest......
>>
>>As always, thanks in advance for all you responses,
>>
>>--
>>R.Ray Walters
>>CTO, Solarray, Inc
>>Nabcep Certified PV Installer,
>>Licensed Master Electrician
>>Solar Design Engineer
>><tel:303%20505-8760>303 505-8760
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>--
>>
>>
>>
>>Mac Lewis
>>
>>"Yo solo sé que no sé nada." -Sócrates
>>
>>
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150821/fff7b805/attachment.htm>
More information about the RE-Wrenches
mailing list