I'm considering an AC coupled system with Enphase that would shed
inverters a group at a time, ending up with one still charging until the
set point is reached. <br><br>
At 12:56 AM 8/21/2015, you wrote:<br>
<blockquote type=cite class=cite cite="">Hi Folks;<br>
<br>
I've done more research on the whole AC coupled issue, and one flaw I
found with both the Sunny Island and the Radian is that they can't really
do a full 3 stage charge for the batteries in off grid mode.<br>
They detect that the batteries are full and disconnect the AC coupled GT
inverters, but this is about as subtle as the very early charge
controllers, and amounts to 1 stage charging.&nbsp; This is fine for
temporary outages, and when the grid comes back, the batteries get a good
3 stage charge.&nbsp; But these folks are really wanting a design that
could be taken off grid permanently.&nbsp;&nbsp; Also as you my recall,
the GT PV system is Enphase, so we can't use the more sophisticated
controls that SMA offers for the Sunny boys. <br>
I hate to say it, but I might be back to a diversion load with PWM
controller.&nbsp; Not elegant, but we could get 3 stage charging.&nbsp;
<br>
Every time I look at AC coupled setups, I just want to start over with
charge controllers. <br><br>
<pre>R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre><font face="Courier New, Courier"></font>On 8/17/2015
9:39 PM, Mac Lewis wrote:<br>
<blockquote type=cite class=cite cite="">Hi Ray, <br><br>
With that size grid-tied system, you would want to use a battery based
inverter(s) near the (6.7/0.8) 8000W range.&nbsp; <br><br>
The frequency shift of the Sunny Islands will work with kicking out the
enphase inverters but you wouldn't get the same output ramping that it
would offer if it was a Sunny Boy grid-tied inverter.&nbsp; The Sunny
Island can effectively solve your generator backfeeding because there is
a reverse current sensor that will disconnect the AC input at whatever
level you want, 50 mA is default I think.&nbsp; You may need to give the
Sunny Island generator start control for this however.<br><br>
You can read about it here on page 137.<br><br>
<a href="http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf">
http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf</a><br><br>
You'll need to give the Sunny Island a digital signal that tell it
whether its connected to a generator or a grid as outlined in the manual.
<br><br>
&nbsp;This is where the Radian is nice because it has two AC Input
terminals.<br><br>
Sounds like an interesting project.<br><br>
Good Luck.<br><br>
<br><br>
<br>
On Mon, Aug 17, 2015 at 8:36 PM, Jerry Shafer
&lt;<a href="mailto:jerrysgarage01@gmail.com">jerrysgarage01@gmail.com</a>
&gt; wrote:<br>

<dl><br>

<dd>I cant see this working well without some battery based
inverter<font color="#888888"><br>

<dd>Jerry<br>
</font>
<dd>On Aug 17, 2015 10:10 AM, &quot;Ray Walters&quot;
&lt;<a href="mailto:ray@solarray.com">ray@solarray.com</a>&gt;
wrote:<br>

<dl>
<dd>HI Esteemed Wrenches:<br><br>

<dd>I am consulting on a system I have never seen, that consists of a
6.7Kw Enphase roof mounted system, and 2 backup generators.&nbsp; Each
generator has an automatic 200 amp transfer switch to back up its own 200
amp panel.&nbsp; Both 200 amp panels are fed by a 400 amp service from
the grid.<br>

<dd>The Enphase PV backfeeds a subpanel in another building which then is
fed by a 2 pole 60 amp breaker in one of the 200 amp panels.<br>

<dd>Currently they are having issues with the generators kicking out
because of the Enphase inverters.&nbsp; That part I understand: you can't
backfeed a generator, or its voltage regulation freaks out.<br><br>

<dd>Now we get to the fun part: they want to create a third critical load
subpanel with loads selected from both 200 amp panels to be powered by
batteries and an inverter.<br>

<dd>I am considering the Sunny Island since it makes the most sense with
its ability to signal the Enphase inverters to shut off when the
batteries are full.&nbsp; I also see this as a partial solution to the
generator issue, since normally the Enphase will be connected to the
output side of the Sunny Island.&nbsp; However, when the generator is
used to charge, we will be back to directly coupling the generator output
to the Enphase.<br>
<br>

<dd>Here are some possible solutions I'm considering:<br>

<dd>1) Use a separate charger for the generator so that it will only feed
DC to the batteries, and not be AC coupled.<br>

<dd>2) convert the PV back to DC with charge controllers, but that would
involve ditching and adding another conduit run between buildings.<br>

<dd>3)&nbsp; Put the Enphase PV on a relay that would disconnect the PV
when charging with the generator.<br>

<dd>4) Something I haven't thought of that one of you clever folks can
suggest......<br><br>

<dd>As always, thanks in advance for all you responses,<br><br>

<dd>-- <br>

<dd>R.Ray Walters<br>

<dd>CTO, Solarray, Inc<br>

<dd>Nabcep Certified PV Installer,<br>

<dd>Licensed Master Electrician<br>

<dd>Solar Design Engineer<br>

<dd><a href="tel:303%20505-8760">303 505-8760</a><br><br>

<dd>_______________________________________________<br>

<dd>List sponsored by Redwood Alliance<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Change listserver email address &amp; settings:<br>

<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>

<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>

<dd>List rules &amp; etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out or update participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>

</dl><br>

<dd>_______________________________________________<br>

<dd>List sponsored by Redwood Alliance<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Change listserver email address &amp; settings:<br>

<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>

<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>

<dd>List rules &amp; etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out or update participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br>

</dl><br><br>
<br>
-- <br><br>
<font color="#305A78"><br>
</font><br>
Mac Lewis<br><br>
<font face="Verdana">&quot;Yo solo s que no s nada.&quot;
-Scrates<br>
</b></font><br><br>
<br>
<pre>_______________________________________________
List sponsored by Redwood Alliance

List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a>

</pre><font face="Courier New, Courier"></font></blockquote><br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" eudora="autourl">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote></body>
</html>