[RE-wrenches] AC Coupled with Generator
Ray Walters
ray at solarray.com
Mon Aug 17 23:26:01 EDT 2015
Yes, we're definitely planning a battery based inverter. The real
trouble is when the generator is charging, its AC power passes through
to the loads and hence to the Enphase inverters.
Also I agree with the other poster about Outback being more cost
effective. I just took a look at their Remote Operated Circuit Breaker
(ROCB) and this looks like a good option.
I've done dump loads before, and never found that to be an elegant
solution. Any other options I should be looking at?
Thanks,
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 8/17/2015 8:36 PM, Jerry Shafer wrote:
>
> I cant see this working well without some battery based inverter
> Jerry
>
> On Aug 17, 2015 10:10 AM, "Ray Walters" <ray at solarray.com
> <mailto:ray at solarray.com>> wrote:
>
> HI Esteemed Wrenches:
>
> I am consulting on a system I have never seen, that consists of a
> 6.7Kw Enphase roof mounted system, and 2 backup generators. Each
> generator has an automatic 200 amp transfer switch to back up its
> own 200 amp panel. Both 200 amp panels are fed by a 400 amp
> service from the grid.
> The Enphase PV backfeeds a subpanel in another building which then
> is fed by a 2 pole 60 amp breaker in one of the 200 amp panels.
> Currently they are having issues with the generators kicking out
> because of the Enphase inverters. That part I understand: you
> can't backfeed a generator, or its voltage regulation freaks out.
>
> Now we get to the fun part: they want to create a third critical
> load subpanel with loads selected from both 200 amp panels to be
> powered by batteries and an inverter.
> I am considering the Sunny Island since it makes the most sense
> with its ability to signal the Enphase inverters to shut off when
> the batteries are full. I also see this as a partial solution to
> the generator issue, since normally the Enphase will be connected
> to the output side of the Sunny Island. However, when the
> generator is used to charge, we will be back to directly coupling
> the generator output to the Enphase.
>
> Here are some possible solutions I'm considering:
> 1) Use a separate charger for the generator so that it will only
> feed DC to the batteries, and not be AC coupled.
> 2) convert the PV back to DC with charge controllers, but that
> would involve ditching and adding another conduit run between
> buildings.
> 3) Put the Enphase PV on a relay that would disconnect the PV
> when charging with the generator.
> 4) Something I haven't thought of that one of you clever folks can
> suggest......
>
> As always, thanks in advance for all you responses,
>
> --
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760 <tel:303%20505-8760>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150817/52b47d00/attachment.htm>
More information about the RE-Wrenches