    Yes, we're definitely planning a battery based inverter.  The real
    trouble is when the generator is charging, its AC power passes
    through to the loads and hence to the Enphase inverters.  <br>
    Also I agree with the other poster about Outback being more cost
    effective.  I just took a look at their Remote Operated Circuit
    Breaker (ROCB) and this looks like a good option.<br>
    I've done dump loads before, and never found that to be an elegant
    solution.  Any other options I should be looking at?<br>
    <br>
    Thanks,<br>
    <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
    <div class="moz-cite-prefix">On 8/17/2015 8:36 PM, Jerry Shafer
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAMUFgmUJ3w01zizY3-CpRM+Tu+a1_zX0LySsLvkLhaNmda455A@mail.gmail.com"
      type="cite">
      <p dir="ltr">I cant see this working well without some battery
        based inverter<br>
        Jerry</p>
      <div class="gmail_quote">On Aug 17, 2015 10:10 AM, "Ray Walters"
        &lt;<a moz-do-not-send="true" href="mailto:ray@solarray.com">ray@solarray.com</a>&gt;
        wrote:<br type="attribution">
        <blockquote class="gmail_quote" style="margin:0 0 0
          .8ex;border-left:1px #ccc solid;padding-left:1ex">HI Esteemed
          Wrenches:<br>
          <br>
          I am consulting on a system I have never seen, that consists
          of a 6.7Kw Enphase roof mounted system, and 2 backup
          generators.  Each generator has an automatic 200 amp transfer
          switch to back up its own 200 amp panel.  Both 200 amp panels
          are fed by a 400 amp service from the grid.<br>
          The Enphase PV backfeeds a subpanel in another building which
          then is fed by a 2 pole 60 amp breaker in one of the 200 amp
          panels.<br>
          Currently they are having issues with the generators kicking
          out because of the Enphase inverters.  That part I understand:
          you can't backfeed a generator, or its voltage regulation
          freaks out.<br>
          <br>
          Now we get to the fun part: they want to create a third
          critical load subpanel with loads selected from both 200 amp
          panels to be powered by batteries and an inverter.<br>
          I am considering the Sunny Island since it makes the most
          sense with its ability to signal the Enphase inverters to shut
          off when the batteries are full.  I also see this as a partial
          solution to the generator issue, since normally the Enphase
          will be connected to the output side of the Sunny Island. 
          However, when the generator is used to charge, we will be back
          to directly coupling the generator output to the Enphase.<br>
          <br>
          Here are some possible solutions I'm considering:<br>
          1) Use a separate charger for the generator so that it will
          only feed DC to the batteries, and not be AC coupled.<br>
          2) convert the PV back to DC with charge controllers, but that
          would involve ditching and adding another conduit run between
          buildings.<br>
          3)  Put the Enphase PV on a relay that would disconnect the PV
          when charging with the generator.<br>
          4) Something I haven't thought of that one of you clever folks
          can suggest......<br>
          <br>
          As always, thanks in advance for all you responses,<br>
          <br>
          -- <br>
          R.Ray Walters<br>
          CTO, Solarray, Inc<br>
          Nabcep Certified PV Installer,<br>
          Licensed Master Electrician<br>
          Solar Design Engineer<br>
          <a moz-do-not-send="true" href="tel:303%20505-8760"
            value="+13035058760" target="_blank">303 505-8760</a><br>
          <br>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          List Address: <a moz-do-not-send="true"
            href="mailto:RE-wrenches@lists.re-wrenches.org"
            target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
            rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a moz-do-not-send="true"
            href="http://www.re-wrenches.org/etiquette.htm"
            rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a moz-do-not-send="true"
            href="http://www.members.re-wrenches.org" rel="noreferrer"
            target="_blank">www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>