[RE-wrenches] Gen preheat in cold climates

Jerry Shafer jerrysgarage01 at gmail.com
Fri Apr 3 14:47:02 EDT 2015


You may want to contact the gen set manufacture to see if the genny can go
cold "freeze protection" at sub zero  because it may be required to operate
24/7in that condition. you may be able to install a thermostat to control
the block heater, this way its not always on.  PS I would use the Outback
products.
Jerry

On Thu, Apr 2, 2015 at 4:47 PM, Gary Higbee <gary at windstreamsolar.com>
wrote:

> Wrenches,
>
> I'm curious what strategies you use to preheat a propane gen in cold
> climates. This is a large off-grid design in a sub-zero winter climate and
> ideal would be to turn on a block heater an hour or two in advance, then
> run the gen cycle. We plan to use either a Schneider XW or Outback Radian
> configuration (still very interested in which you'd use and why). We could
> set up a logic/relay system to first send the gen request to the heater for
> a while and then turn off and initiate a gen cycle but that would eliminate
> the ability for autostart on short notice. I've read of heat lamps on a
> thermostat, just wondering if you have seen other solutions.
>
> Thanks!
>
> Gary
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150403/0c773725/attachment.htm>


More information about the RE-Wrenches mailing list