[RE-wrenches] 3 phase battery inverters
Drake
drake.chamberlin at redwoodalliance.org
Thu Jul 24 10:38:37 EDT 2014
Hi Jay,
I had to deal with this once on a Trace SW
system. The cheapest option turned out to be to
just adding another inverter, not synchronized,
on the third leg of the generator.
All loads were 120/240, so no need for 208.
Commercial battery chargers were way expensive.
The non synchronized inverter charged batteries
just fine, and was used with a separate panel to
feed a few tough loads that could have caused the
lights to dim on surge. The three phase generator
windings were reasonably well balanced with this setup.
Drake
At 06:15 AM 7/24/2014, you wrote:
>If the client does not need three phase but has
>a three phase generator, you can rewire the
>alternator to single phase, or have it done by a generator tech.
>
>
>On Wed, Jul 23, 2014 at 10:35 PM, jay peltz
><<mailto:jay at asis.com>jay at asis.com> wrote:
>Hi Guys,
>
>Yes that could work, but then you wouldn't have
>genny backup, which isn't a good idea IMHO.
>
>I'm still researching if the client really needs 3 phase or not.
>
>thanks all,
>
>jay
>
>
>
>
>On Jul 23, 2014, at 4:21 PM, Chris Mason wrote:
>
>>Are the loads three phase or just the generator?
>>
>>
>>On Wed, Jul 23, 2014 at 6:05 PM, Jerry Shafer
>><<mailto:jerrysgarage01 at gmail.com>jerrysgarage01 at gmail.com> wrote:
>>
>>Outback for sure but I have not seen the sw
>>line work on 3 ph nore the SI's I will say OB
>>work well. You may also want to consider a 3 ph
>>battery charger and a regular l120/240 battery system just a thought
>>On Jul 23, 2014 11:06 AM, "Jay Peltz"
>><<mailto:jay at asis.com>jay at asis.com> wrote:
>>>Hi all
>>
>>I have a client who
>>Might need 3 phase battery based inverters for 208/120 US 60 hz.Â
>>I believe the choices are: Â SI, XW( with
>>reprogramming) and outback FX line.Â
>>
>>This is not for motors, but running off of a 3 phase generator.Â
>>
>>Anything I've missed?
>>
>>Jay
>>Peltz power
>>
>>PS thanks for all the comments as to my previous questions on batteries.Â
>>J
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>>
>>
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>--
>>Chris Mason
>>NABCEP Certified Solar PV Installer
>>Solar Design Engineer
>>Generac Generators Industrial technician
>>
>><http://www.cometenergysystems.com/>www.cometsolar.com
>><tel:264.235.5670>264.235.5670
>><tel:869.662.5670>869.662.5670
>>Skype: netconcepts
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>
>
>
>--
>Chris Mason
>NABCEP Certified Solar PV Installer
>Solar Design Engineer
>Generac Generators Industrial technician
>
><http://www.cometenergysystems.com>www.cometsolar.com
>264.235.5670
>869.662.5670
>Skype: netconcepts
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140724/7d926d63/attachment.htm>
More information about the RE-Wrenches
mailing list