Hi Jay,<br><br>
I had to deal with this once on a Trace SW system. The cheapest option
turned out to be to just adding another inverter, not synchronized, on
the third leg of the generator. <br><br>
All loads were 120/240, so no need for 208. Commercial battery chargers
were way expensive. The non synchronized inverter charged batteries just
fine, and was used with a separate panel to feed a few tough loads that
could have caused the lights to dim on surge. The three phase generator
windings were reasonably well balanced with this setup. <br><br>
Drake<br><br>
<br>
At 06:15 AM 7/24/2014, you wrote:<br>
<blockquote type=cite class=cite cite="">If the client does not need
three phase but has a three phase generator, you can rewire the
alternator to single phase, or have it done by a generator tech.<br><br>
<br>
On Wed, Jul 23, 2014 at 10:35 PM, jay peltz
<<a href="mailto:jay@asis.com">jay@asis.com</a>> wrote:<br>
<dl>
<dd>Hi Guys,<br><br>
<dd>Yes that could work, but then you wouldn't have genny backup, which
isn't a good idea IMHO.<br><br>
<dd>I'm still researching if the client really needs 3 phase or
not.<br><br>
<dd>thanks all,<br><br>
<dd>jay<br><br>
<br><br>
<br>
<dd>On Jul 23, 2014, at 4:21 PM, Chris Mason wrote:<br><br>
<blockquote type=cite class=cite cite="">
<dd>Are the loads three phase or just the generator?<br><br>
<br>
<dd>On Wed, Jul 23, 2014 at 6:05 PM, Jerry Shafer
<<a href="mailto:jerrysgarage01@gmail.com">jerrysgarage01@gmail.com</a>
> wrote:<br>
<dl><br>
<dd>Outback for sure but I have not seen the sw line work on 3 ph nore
the SI's I will say OB work well. You may also want to consider a 3 ph
battery charger and a regular l120/240 battery system just a thought
<br>
<dd>On Jul 23, 2014 11:06 AM, "Jay Peltz"
<<a href="mailto:jay@asis.com">jay@asis.com</a>> wrote:<br>
<blockquote type=cite class=cite cite="">
<dl>
<dd>Hi all</blockquote><br>
<dd>I have a client who<br>
<dd>Might need 3 phase battery based inverters for 208/120 US 60 hz.
<br>
<dd>I believe the choices are: SI, XW( with reprogramming) and outback
FX line. <br><br>
<dd>This is not for motors, but running off of a 3 phase generator.
<br><br>
<dd>Anything I've missed?<br><br>
<dd>Jay<br>
<dd>Peltz power<br><br>
<dd>PS thanks for all the comments as to my previous questions on
batteries. <br>
<dd>J<br><br>
<dd>_______________________________________________<br>
<dd>List sponsored by Redwood Alliance<br><br>
<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>
<dd>Change listserver email address & settings:<br>
<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
<dd>List rules & etiquette:<br>
<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>
<dd>Check out or update participant bios:<br>
<dd><a href="http://www.members.re-wrenches.org/">
www.members.re-wrenches.org</a><br><br>
<br>
</dl><br>
<dd>_______________________________________________<br>
<dd>List sponsored by Redwood Alliance<br><br>
<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>
<dd>Change listserver email address & settings:<br>
<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
<dd>List rules & etiquette:<br>
<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>
<dd>Check out or update participant bios:<br>
<dd><a href="http://www.members.re-wrenches.org/">
www.members.re-wrenches.org</a><br><br>
<br>
</dl><br><br>
<br>
<dd>-- <br>
<dd>Chris Mason<br>
<dd>NABCEP Certified Solar PV Installer<br>
<dd>Solar Design Engineer<br>
<dd>Generac Generators Industrial technician<br><br>
<dd><a href="http://www.cometenergysystems.com/">www.cometsolar.com</a>
<br>
<dd><a href="tel:264.235.5670">264.235.5670</a><br>
<dd><a href="tel:869.662.5670">869.662.5670</a><br>
<dd>Skype: netconcepts<br>
<dd>_______________________________________________<br>
<dd>List sponsored by Redwood Alliance<br><br>
<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>
<dd>Change listserver email address & settings:<br>
<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
<dd>List rules & etiquette:<br>
<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>
<dd>Check out or update participant bios:<br>
<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br>
</blockquote><br><br>
<dd>_______________________________________________<br>
<dd>List sponsored by Redwood Alliance<br><br>
<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>
<dd>Change listserver email address & settings:<br>
<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br>
<br>
<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
<dd>List rules & etiquette:<br>
<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>
<dd>Check out or update participant bios:<br>
<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br>
</dl><br><br>
<br>
-- <br>
Chris Mason<br>
NABCEP Certified Solar PV Installer<br>
Solar Design Engineer<br>
Generac Generators Industrial technician<br><br>
<a href="http://www.cometenergysystems.com">www.cometsolar.com</a><br>
264.235.5670<br>
869.662.5670<br>
Skype: netconcepts<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" eudora="autourl">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote></body>
</html>