[RE-wrenches] Busbar 120% rule
Nathan Charles
ncharles at paradiseenergysolutions.com
Thu Mar 27 15:15:09 EDT 2014
Also in 2014 we get 705.12(D)(2)(3)(c) which should be very useful in
distribution panelboards.
-N
On Thu, Mar 27, 2014 at 3:00 PM, Brian Mehalic <brian at solarenergy.org>wrote:
> The "120% rule" in 2014 is 705.12(D)(2)(3)(b). Ugh. Anyway, the inverter
> current is "125 percent of the inverter(s) output circuit current", aka the
> minimum OCPD and conductor ampacity value per 705.60(B) and 690.8(B)(1).
>
> This is actually a bit of wiggle room: in 2011 the 120% rule was based on
> the inverter output circuit OCPD size, which is often larger than 125% of
> the inverter output circuit current.
>
> Cheers,
>
>
> Brian Mehalic
> NABCEP Certified Solar PV Installation Professional(tm) R031508-59
> IREC ISPQ Certified Affiliated Instructor/PV US-0132
>
> PV Curriculum Developer and Instructor
> Solar Energy International
> http://www.solarenergy.org
>
>
> On Thu, Mar 27, 2014 at 2:34 PM, Troy Harvey <taharvey at heliocentric.org>wrote:
>
>> I am wondering about the busbar 120% rule, and if there is any wiggle
>> room in the 2014 NEC.
>>
>> Fundamentally I don't understand the 120% rule. If my solar breaker is
>> installed properly at the bottom of the busbar, and the grid-tie breaker is
>> installed at the top, and the busbar itself is rated for 120% of the panel
>> rating, I don't see any means by which a solar breaker of a size
>> substantially larger than 120% could cause a problem. There can be no
>> place on the busbar under any situation (that I can think of) that would
>> exceed 120% because the supply current is coming from opposite ends of the
>> bus bar - even in the worst case load situation. So even if I had a huge PV
>> system (100A), backfeeding the bottom of a 200A panel, I don't see a
>> situation where there is more than 200A over any one section of busbar. Am
>> I wrong, or is the NEC just too prescriptive for its own good?
>>
>> Also would you say that the 120% is based on the inverter max output or
>> backfeed breaker size?
>>
>>
>> thanks,
>>
>> Troy Harvey
>> ---------------------
>> Principal Engineer
>> Heliocentric
>> 801-453-9434
>> taharvey at heliocentric.org
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
--
Nathan Charles
Engineer
NABCEP Certified PV Installation Professional #042013-20
Paradise Energy Solutions
(717) 283-2021 direct
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140327/ec67608c/attachment-0001.htm>
More information about the RE-Wrenches