<div dir="ltr">Also in 2014 we get 705.12(D)(2)(3)(c) which should be very useful in distribution panelboards.<div><br></div><div>-N</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Mar 27, 2014 at 3:00 PM, Brian Mehalic <span dir="ltr">&lt;<a href="mailto:brian@solarenergy.org" target="_blank">brian@solarenergy.org</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">The &quot;120% rule&quot; in 2014 is 705.12(D)(2)(3)(b). &nbsp;Ugh. &nbsp;Anyway, the inverter current is &quot;125 percent of the inverter(s) output circuit current&quot;, aka the minimum OCPD and conductor ampacity value per 705.60(B) and 690.8(B)(1).<div>

<br></div><div>This is actually a bit of wiggle room: in 2011 the 120% rule was based on the inverter output circuit OCPD size, which is often larger than 125% of the inverter output circuit current.</div><div><br></div>
<div>
Cheers,</div></div><div class="gmail_extra"><br clear="all"><div><div dir="ltr"><div><br></div><div>Brian Mehalic <br>NABCEP Certified Solar PV Installation Professional&trade;&nbsp;R031508-59<div>IREC ISPQ Certified Affiliated Instructor/PV US-0132<br>

<div><br></div><div>PV Curriculum Developer and Instructor<div>Solar Energy International<br><a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div></div></div>
<br><br><div class="gmail_quote"><div><div class="h5">On Thu, Mar 27, 2014 at 2:34 PM, Troy Harvey <span dir="ltr">&lt;<a href="mailto:taharvey@heliocentric.org" target="_blank">taharvey@heliocentric.org</a>&gt;</span> wrote:<br>
</div></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div class="h5">
<div style="word-wrap:break-word"><div>I am wondering about the busbar 120% rule, and if there is any wiggle room in the 2014 NEC.</div><div><br></div><div>Fundamentally I don&#39;t understand the 120% rule. If my solar breaker is installed properly at the bottom of the busbar, and the grid-tie breaker is installed at the top, and the busbar itself is rated for 120% of the panel rating, I don&#39;t see any means by which a solar breaker of a size substantially larger than 120% &nbsp;could cause a problem. There can be no place on the busbar under any situation (that I can think of) that would exceed 120% because the supply current is coming from opposite ends of the bus bar - even in the worst case load situation. So even if I had a huge PV system (100A), backfeeding the bottom of a 200A panel, I don&#39;t see a situation where there is more than 200A over any one section of busbar. Am I wrong, or is the NEC just too prescriptive for its own good?</div>

<div><br></div><div>Also would you say that the 120% is based on the inverter max output or backfeed breaker size?</div><div><br></div><div><br></div><div>
<span style="border-spacing:0px;line-height:normal;text-indent:0px;border-collapse:separate;letter-spacing:normal;text-align:-webkit-auto;font-variant:normal;text-transform:none;white-space:normal;word-spacing:0px"><div style="word-wrap:break-word">

<span style="font-size:11px">thanks,<br><br>Troy Harvey<br>---------------------<br>Principal Engineer<br>Heliocentric<br><a href="tel:801-453-9434" value="+18014539434" target="_blank">801-453-9434</a><br><a href="mailto:taharvey@heliocentric.org" target="_blank">taharvey@heliocentric.org</a><br>

</span><br><br></div></span>
</div>
<br></div><br></div></div><div class="">_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></div></blockquote></div><br></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div dir="ltr">Nathan Charles<div>Engineer<br><div>NABCEP Certified PV Installation Professional #042013-20</div></div><div>Paradise Energy Solutions</div>
<div>(717) 283-2021 direct</div></div>
</div>