[RE-wrenches] Fault Current

Chris Mason cometenergysystems at gmail.com
Thu Mar 27 14:22:21 EDT 2014


Before I spent any money, I would hire a PE with solar experience to give
you an option. I doubt solar iinverters, which are current limited, would
be a fault current issue. Usually fault current rating is a factor of the
internal resistance of the secondary winding of a high voltage transformer.
Solar inverters can't produce those kind of short circuit currents and are
not a factor.


On Thu, Mar 27, 2014 at 2:05 PM, Karl Jaeger <kjaeger at lightwavesolar.com>wrote:

>  Esteemed Wrenches,
>
> We've recently run into an issue with a local distributor citing network
> fault current on a split-phase service as a reason to prevent
> interconnection of our customer's solar array. They've given us the options
> of reducing our system size from 36.5kW-DC to 15kW-DC, or having the
> customer upgrade to 3-phase at a soft price of $20-30K. We're looking at
> 32kW of inverters on a 167kVA transformer.
>
>
>
> Does anyone have experience on circumventing the issue of network fault
> current? Any experience with Fault Current Limiters?
>
>
>
> Much appreciated,
>
>
>
> *Karl Jaeger*
>
> *Design/Build Engineer*
>
> *LightWave Solar Electric LLC*
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140327/7c4a6125/attachment-0001.htm>


More information about the RE-Wrenches mailing list