[RE-wrenches] Fault Current
Dave Click
daveclick at fsec.ucf.edu
Thu Mar 27 14:28:55 EDT 2014
Karl, you're interconnecting into a spot/area network, right? It's a
real concern; some solutions and background on the issue here:
http://www.nrel.gov/docs/fy09osti/45061.pdf
DKC
On 2014/3/27, 14:05, Karl Jaeger wrote:
>
> Esteemed Wrenches,
>
> We've recently run into an issue with a local distributor citing
> network fault current on a split-phase service as a reason to prevent
> interconnection of our customer's solar array. They've given us the
> options of reducing our system size from 36.5kW-DC to 15kW-DC, or
> having the customer upgrade to 3-phase at a soft price of $20-30K.
> We're looking at 32kW of inverters on a 167kVA transformer.
>
> Does anyone have experience on circumventing the issue of network
> fault current? Any experience with Fault Current Limiters?
>
> Much appreciated,
>
> *Karl Jaeger*
>
> *Design/Build Engineer*
>
> *LightWave Solar Electric LLC*
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140327/97cf4dfa/attachment.htm>
More information about the RE-Wrenches
mailing list