[RE-wrenches] Trojan IND9-6V settings with Outback FX and Flexmax 60

jay peltz jay at asis.com
Thu Feb 20 18:33:49 EST 2014


HI Larry,

Yep totally confusing about their overview information, and they are working on it to get it more clear.
The specific spec sheets are accurate though.

jay


On Feb 20, 2014, at 3:49 PM, Larry Crutcher, Starlight Solar Power Systems wrote:

> Hey Jay,
> 
> What do you have that is different than what I said? Attached is the IND9 data sheet. It shows 2.35 to 2.45 for absorb. I was pointing out that there is confusion: Trojan has multiple publications with different numbers on them.
> 
> Larry
> <Screen Shot 2014-02-20 at 1.52.07 PM.png>
> 
> 
> On Feb 20, 2014, at 9:46 AM, jay peltz <jay at asis.com> wrote:
> 
> HI Larry,
> 
> I was very curious about your charge specs as they didn't agree with what I have.
> I have contacted Trojan and the specs you show below are for their "signature" line and not the IND line.
> 
> The official word on max C rate is 10-13% of max battery capacity for IND line.
> The vpc voltages are in their IND product literature.
> 
> jay
> 
> peltz power
> 