Hey Jay,
What do you have that is different than what I said? Attached is the IND9 data sheet. It shows 2.35 to 2.45 for absorb. I was pointing out that there is confusion: Trojan has multiple publications with different numbers on them.
Larry
On Feb 20, 2014, at 9:46 AM, jay peltz <jay at asis.com> wrote:
HI Larry,
I was very curious about your charge specs as they didn't agree with what I have.
I have contacted Trojan and the specs you show below are for their "signature" line and not the IND line.
The official word on max C rate is 10-13% of max battery capacity for IND line.
The vpc voltages are in their IND product literature.
jay
peltz power
On Feb 19, 2014, at 2:28 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
> Hi Chris,
>
> Moving from VRLA to flooded, the customer should know it takes about 20% more energy and longer charge time to get to 100% SoC.
>
> Trojan states that charge current should not be more than 10-13% of C20 discharge rate. For the IND9, that's 46 to 60 amps maximum per string. VRLA can handle MUCH more.
>
> Since sun-hours per day is the same and you need more energy to get 100%, more PV solar or more generator time may be required.
>
> I have seen 3 different published specifications from Trojan Battery about charging their cells. One publication lists 2.45 to 2.79 Vpc. 2.79 volts!! Does anyone charge this high? I'm a fan of high voltage charging, but I generally don't go over 2.53 Vpc for flooded. But, since the IND9 data sheet lists 2.45 Vpc maximum, I'de stick with that.
>
> Larry
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140220/80d0af68/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Screen Shot 2014-02-20 at 1.52.07 PM.png
Type: image/png
Size: 90330 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140220/80d0af68/attachment.png>
More information about the RE-Wrenches
mailing list