Ray and August:
Thanks for the speedy reply. I did confuse M250s with the M215s. The
actual inverters to be used are the M215s.
I swear I had a spec sheet for the M190 that showed 0.75 A but I can't find
it anymore. So using 0.8A:
9 * 0.8A = 7.2A
10 * .9A = 9.0A
Total = 16.2
De-rate: 16.2*1.25 = 20.25.
Maybe that will fly.
The other question is: I don't have to use the value of the three breakers
in the Solar load center to calculate my POC in the M/M/C? The code says:
The sum of the ampere ratings of overcurrent devices feeding a busbar or
conductor shall not exceed 120% of the rating of the busbar or conductor. I
am assuming I don't have to add the two 15s and the 20 and use that in
figuring the back feed to the M/M/C since the M/MC is fed by a 20.
Thanks so much for your help. I am going to send this on to the lead
inspector for the County. I am fortunate that he has always been willing to
review these problems and flexible where appropriate, at least in my view.
Sincerely,
William Miller
PS: I update the drawing.
Wm
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of August Goers
Sent: Wednesday, October 09, 2013 3:40 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Point of connection question
William,
You have 9 M190s each running at 800 mA according to spec sheet. That equals
7.2 A nominal output current. Plus you have 10 M250s (if you look at your
drawing) each running at 1 A = 10 A. 7.2 A + 10 A = 17.2 A * 1.25 = 21.5 A
min breaker size. So, you'll need to round your breaker to a 25 A or 30 A
breaker in the sub. You don't have any problem in the sub panel but the
meter main is going to be a problem if it is a 100 A meter/main.
Your drawing and case study notes don't seem to correspond - you mention
M215s in the case study and show M250s on the drawing. If you indeed have 10
M215s then you're at 10 * 0.9 A = 9 A. 7.2 A + 9 A = 16.2 A * 1.25 = 20.25 A
min breaker size. This is where it gets tricky. My fellow engineer just
pointed out NEC 220.5(B) which allows you to drop fractions of amperes less
than 0.5. So, I think you'd be okay with a 20 A solar breaker in this case.
Best, August
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Wednesday, October 09, 2013 3:07 PM
To: RE-wrenches
Subject: [RE-wrenches] Point of connection question
Friends:
At the risk of asking a question that may have been asked and answered here
in the past, I wish to pose a question about Point of Connection.
Rather than outline the situation here I put it all on a web page. If any
of you have a moment to review this, I would be most appreciative.
http://www.millersolar.com/MillerSolar/case_studies/POC/_POC_Question.html
Thanks in advance,
William Miller
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4142 / Virus Database: 3604/6722 - Release Date: 10/04/13
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20131009/d1894ddc/attachment-0001.htm>
More information about the RE-Wrenches
mailing list