[RE-wrenches] Point of connection question

August Goers august at luminalt.com
Wed Oct 9 18:40:00 EDT 2013


William,



You have 9 M190s each running at 800 mA according to spec sheet. That
equals 7.2 A nominal output current. Plus you have 10 M250s (if you look at
your drawing) each running at 1 A = 10 A. 7.2 A + 10 A = 17.2 A * 1.25 =
21.5 A min breaker size. So, you'll need to round your breaker to a 25 A or
30 A breaker in the sub. You don't have any problem in the sub panel but
the meter main is going to be a problem if it is a 100 A meter/main.



Your drawing and case study notes don't seem to correspond - you mention
M215s in the case study and show M250s on the drawing. If you indeed have
10 M215s then you're at 10 * 0.9 A = 9 A. 7.2 A + 9 A = 16.2 A * 1.25 =
20.25 A min breaker size. This is where it gets tricky. My fellow engineer
just pointed out NEC 220.5(B) which allows you to drop fractions of amperes
less than 0.5. So, I think you'd be okay with a 20 A solar breaker in this
case.



Best, August



*From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *William Miller
*Sent:* Wednesday, October 09, 2013 3:07 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Point of connection question



Friends:



At the risk of asking a question that may have been asked and answered here
in the past, I wish to pose a question about Point of Connection.



Rather than outline the situation here I put it all on a web page.  If any
of you have a moment to review this, I would be most appreciative.



http://www.millersolar.com/MillerSolar/case_studies/POC/_POC_Question.html



Thanks in advance,



William Miller
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20131009/5fab5dc8/attachment.htm>


More information about the RE-Wrenches mailing list