[RE-wrenches] Combining Enphase M190 and M215 on same circuit
Kent Osterberg
kent at coveoregon.com
Sun May 19 10:38:47 EDT 2013
Jason,
The M190 requires using a 15-amp (maximum) branch circuit. As long as
the total current from both types of inverters doesn't exceed 12 amps
(80% of 15), there should not be a problem in mixing the inverters. The
combination you are proposing is only 8.6 amps -- it should be fine.
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
On 5/18/2013 3:26 PM, Jason Szumlanski wrote:
> Is there any reason I can't do this? I have an existing string of 3
> M190's and want to add 7 M215's. I plan to tie into the same j-box,
> which has #10 going to a fusible disconnect and a supply side tap.
> I'll just have to change the fuse rating.
>
> Any comm issues reported with this setup?
>
> Jason Szumlanski
> Fafco Solar
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130519/318bc325/attachment-0001.htm>
More information about the RE-Wrenches
mailing list