    <div class="moz-cite-prefix">Jason,<br>
      <br>
      The M190 requires using a 15-amp (maximum) branch circuit. As long
      as the total current from both types of inverters doesn't exceed
      12 amps (80% of 15), there should not be a problem in mixing the
      inverters. The combination you are proposing is only 8.6 amps --
      it should be fine.<br>
      <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
</pre>
      On 5/18/2013 3:26 PM, Jason Szumlanski wrote:<br>
    </div>
    <blockquote
      cite="mid:5460FD315F814296B54F904A50C13BDE@fafcosolar.com"
      type="cite">
      <div id="reply-content"> Is there any reason I can't do this? I
        have an existing string of 3 M190's and want to add 7 M215's. I
        plan to tie into the same j-box, which has #10 going to a
        fusible disconnect and a supply side tap. I'll just have to
        change the fuse rating.&nbsp; </div>
      <div id="reply-content"><br>
      </div>
      <div id="reply-content">Any comm issues reported with this setup?</div>
      <div id="F1903E78041B4AFAA23ADE4FF6BBCD04">
        <div><br>
        </div>
        Jason Szumlanski<br>
        Fafco Solar<br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>