William - You're correct, I was confused - thanks for setting me straight!
Regards, Gary
On 3/1/13 1:05 PM, William Miller wrote:
> Gary:
>
> I think you are a little confused about the operating modes of the XW
> inverter:
>
> In the AC Passthru mode, no battery charging occurs. Below is the
> passage from the manual that describes this:
>
> /The AC connected to the AC1 or AC2 input is passing directly through
> the Xantrex XW
> Series Inverter/Charger to the loads. The batteries are not being
> charged in this state.
>
> /In the normal transfer mode, battery charging does occur. It is my
> clear understanding that the Xantrex SW and XW inverters and the
> Outback FX and Radian inverters will regulate battery charging so that
> the charger circuit uses only excess amperage available. For
> example: If the input breaker size is programmed for 60 amps and
> there is 60 amps of load, 0 amps of AC will be used for battery
> charging. If the load decreases to 50 amps, 10 amps of AC will be
> used for battery charging, etc.. Therefore, the OCPD does _not_ need
> to be sized to accommodate both uses of input AC.
>
> Below is a passage from the XW Operating Manual that describes this:
>
> /In addition, the battery charger can reduce its charging current to
> the batteries
> so the combined charge AC current and total load current does not
> exceed the
> capacity of the generator or trip its output breakers or fuses.
>
> /Extending this discussion beyond the current topic (pun intended), we
> need to understand what happens if the connected loads exceed the
> input breaker rating. Here the game changes. The FX inverter can not
> prevent the overload from passing to the input breaker, possibly
> tripping it. The SW, XW and Radian inverters can provide "Generator
> Support." Do not confuse Generator Support with Generator Remote
> start functions. Generator Support allows the inverter to sync to,
> and assist the AC input source in powering loads. To use the example
> above: If the load rises to 70 amps, the inverter draws energy from
> the batteries to provide the last 10 amps.
>
> Below is the passage from the XW manual that describes this:
>
> /AC2 Breaker: Sets the AC2 (Gen) breaker size, based on the size of
> the installed AC breaker. The
> breaker size must not exceed the capacity of the generator. The
> Xantrex XW Series
> Inverter/Charger limits the maximum input current to this setting by
> derating its charging
> current to an equivalent of 80% of the AC breaker size. If the
> connected loads exceed the
> AC2 breaker setting, the AC breaker trips. The breaker may not trip if
> Gen Support is
> enabled and Gen Amps is configured not to exceed the generator's rated
> output current.
>
> /I hope this information is relevant, correct and helpful.
>
> Sincerely,
>
> William Miller
>
>
>
>
> At 08:24 AM 3/1/2013, you wrote:
>> Larry:
>>
>> In the case of the Xantrex XW Series, while in the "AC Pass-Thru"
>> Mode, the internal transfer switch relay connects the protected loads
>> directly to the AC1 grid input. The XW internal battery charger is
>> then activated to recharge the battery bank.
>>
>> The OCPD(s) through which the protected load amps and charging amps
>> are passing must be sized to accommodate both at the same time.
>>
>> Regards,
>>
>> Gary Willett
>> Icarus Solar
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130303/90251141/attachment-0001.htm>
More information about the RE-Wrenches
mailing list