    <div class="moz-cite-prefix">William - You're correct, I was
      confused - thanks for setting me straight!<br>
      <br>
      Regards,&nbsp; Gary<br>
      <br>
      On 3/1/13 1:05 PM, William Miller wrote:<br>
    </div>
    <blockquote
      cite="mid:6.0.1.1.2.20130301103756.02f91ec0@millersolar.com"
      type="cite">
      Gary:<br>
      <br>
      I think you are a little confused about the operating modes of the
      XW
      inverter:<br>
      <br>
      In the AC Passthru mode, no battery charging occurs.&nbsp; Below is the
      passage from the manual that describes this:<br>
      <br>
      <i>The AC connected to the AC1 or AC2 input is passing directly
        through
        the Xantrex XW<br>
        Series Inverter/Charger to the loads. The batteries are not
        being charged
        in this state.<br>
        <br>
      </i>In the normal transfer mode, battery charging does occur.&nbsp; It
      is
      my clear understanding that the Xantrex SW and XW inverters and
      the
      Outback FX and Radian inverters will regulate battery charging so
      that
      the charger circuit uses only excess amperage available.&nbsp; For
      example:&nbsp; If the input breaker size is programmed for 60 amps and
      there is 60 amps of load, 0 amps of AC will be used for battery
      charging.&nbsp; If the load decreases to 50 amps, 10 amps of AC will be
      used for battery charging, etc..&nbsp; Therefore, the OCPD does
      <u>not</u> need to be sized to accommodate both uses of input
      AC.<br>
      <br>
      Below is a passage from the XW Operating Manual that describes
      this:<br>
      <br>
      <i>In addition, the battery charger can reduce its charging
        current to
        the batteries<br>
        so the combined charge AC current and total load current does
        not exceed
        the<br>
        capacity of the generator or trip its output breakers or fuses.<br>
        <br>
      </i>Extending this discussion beyond the current topic (pun
      intended), we
      need to understand what happens if the connected loads exceed the
      input
      breaker rating.&nbsp; Here the game changes.&nbsp; The FX inverter can
      not prevent the overload from passing to the input breaker,
      possibly
      tripping it.&nbsp; The SW, XW and Radian inverters can provide
      "Generator Support."&nbsp; Do not confuse Generator Support
      with Generator Remote start functions.&nbsp; Generator Support allows
      the
      inverter to sync to, and assist the AC input source in powering
      loads.&nbsp; To use the example above:&nbsp; If the load rises to 70
      amps, the inverter draws energy from the batteries to provide the
      last 10
      amps. <br>
      <br>
      Below is the passage from the XW manual that describes this:<br>
      <br>
      <i>AC2 Breaker:&nbsp; Sets the AC2 (Gen) breaker size, based on the
        size
        of the installed AC breaker. The<br>
        breaker size must not exceed the capacity of the generator. The
        Xantrex
        XW Series<br>
        Inverter/Charger limits the maximum input current to this
        setting by
        derating its charging<br>
        current to an equivalent of 80% of the AC breaker size. If the
        connected
        loads exceed the<br>
        AC2 breaker setting, the AC breaker trips. The breaker may not
        trip if
        Gen Support is<br>
        enabled and Gen Amps is configured not to exceed the generator&#8217;s
        rated
        output current.<br>
        <br>
      </i>I hope this information is relevant, correct and helpful.<br>
      <br>
      Sincerely,<br>
      <br>
      William Miller<br>
      <br>
      <br>
      <br>
      <br>
      At 08:24 AM 3/1/2013, you wrote:<br>
      <blockquote type="cite" class="cite" cite="">Larry:<br>
        <br>
        In the case of the Xantrex XW Series, while in the "AC
        Pass-Thru" Mode, the internal transfer switch relay connects the
        protected loads directly to the AC1 grid input. The XW internal
        battery
        charger is then activated to recharge the battery bank.<br>
        <br>
        The OCPD(s) through which the protected load amps and charging
        amps are
        passing must be sized to accommodate both at the same time.<br>
        <br>
        Regards,<br>
        <br>
        Gary Willett<br>
        Icarus Solar</blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>