Hi Dan,
The Iota jumper only raises voltage by 0.6 volts above the default setting. You will need to insert the jumper AND adjust the voltage POT (now internal) to reach the EQ range.
For off grid systems, I usually turn up the Iota voltage POT fully since generator run time is rarely enough to cause a long over-voltage condition. Then when the customer wants to equalize, just continue running the generator. Sometimes I install a toggle switch in series with the jumper in case a lower voltage is desired.
Larry Crutcher
Starlight Solar Power Systems
On Jan 28, 2013, at 7:41 AM, Dan Fink wrote:
Carl;
The Iotas we are using have an external jumper that you insert that allows it to get to EQ voltage.
DAN