Carl;

The Iotas we are using have an external jumper that you insert that allows
it to get to EQ voltage.

DAN


On Sun, Jan 27, 2013 at 7:31 PM, Carl Hansen <solarwks at cybermesa.com> wrote:

>   Dan,
>    You may be do this as well, but I frequently deal with homeowners with
> inexpensive generators, I find that the Outback and Magnum inverters are
> very tolerant but I do generally have to load the generator up to where I
> want it bulk charging the batteries, then adjust the generator speed to
> dial in the freqency to 60Hz using the throttle adj.  screw.
>    Do you find the Iota chargers can reach bulk charge voltages, or even
> EQ voltages ?
>