Thank you to all who responded to this post.

Larry, that sounds like a great potential solution. That will put the 
frequency shift in line with where the battery cutoff voltage needs 
to be. The frequency shift happens 2 volts above the absorption 
charge set point. My only issue with the solution is the 1 1/2 hour 
round trip to the site (it could be worse).  Maybe Concorde can give 
me information that will allow me to set up the charge parameters 
without having to tweak.

Allan, dump loads are a great way to go, for sure. The tech I spoke 
to at Magnum recommended the relay as a fail safe for the frequency 
shift.  When the issue of the inverter frequency shifting at 2 volts 
above the absorption charge set point came up, the relay became the 
primary protective device for the AGM batteries.

We didn't use diversion loads since this is a backup system, and will 
probably only operate a few days per year.  The inverter should 
maintain the batteries rather than the solar. We used the Morningstar 
relay driver, in part, to allow dump loads to be added if desired.

Another solution was offered by APRS World, LLC.  They likely can 
build products that would trigger relays using the temperature 
compensated data from the Magnum Network.

It would sure simplify life it Magnum could add an axillary 
relay.  Would that require putting the inverter, or entire line of 
inverters, back into UL for re-approval?

Drake


At 05:36 PM 3/7/2013, you wrote:
>Meant to say, "You should tweak #3 & #4 above..."
>
>
>Drake,
>
>Charging an AGM battery does not have to occur at the maximum charge 
>voltage allowable; you can charge at a lower voltage for longer 
>periods of time and still achieve 100% SoC. Since you have grid 
>power to work with, slow down the charge cycle.
>
>Assuming you have a late model ME-RC and version 5 or higher 
>inverter, you can custom program the charge voltages. Here's what I would do:
>    * Go to Custom settings for battery type (setup menu 04).
>    * Set the Absorb voltage for 26.8.
>    * Set the Float for 26.4
>    * Set the absorb time to 8 hours
>    * Be sure the charge rate( setup menu 05) is 100%.
>
>Near the end of the absorb charge cycle, measure the current going 
>into the battery. If it is less than 0.2 amps/100AH capacity, the 
>bank is full. You should #3 & #4 above until it works out for the 
>low temp. comp. and charge time but it should work well.
>
>If you are concerned about this lower voltage, set up a periodic 
>equalize charge to 28.8.
>
>Larry Crutcher
>Starlight Solar Power Systems
>
>
>
>
>
>On Mar 7, 2013, at 3:00 PM, Drake wrote:
>
>Hello Wrenches,
>
>I had an unexpected glitch in AC coupling a Magnum 4024 PAE 
>inverter.  The system utilizes AGM batteries, which (according to 
>Concorde tech support) have a very strict upper voltage limit.
>
>The relay used to stop the current input from the direct grid tie 
>inverter, when battery voltage is high, is controlled by a 
>Morningstar Relay Driver.  The relay driver is set to shut off the 
>charge at 28.8 volts.
>
>The charger on the Magnum is set to charge the batteries to  28.6 volts.
>
>The plan was to be able to charge batteries from the Magnum without 
>tripping the AC connection between the grid tie inverter to the 
>grid.  The Magnum should charge to 28.6 volts, 0.2 volts below the 
>relay driver's programmed trigger point.
>
>There is one catch to using this approach. The Magnum inverter has a 
>remote temperature sensor in the battery bank. The relay driver is 
>not temperature corrected. Therefore, when the batteries are cold, 
>the charging voltage goes up in the Magnum.  This higher voltage 
>trips the relay controlled by the driver, and disconnects the grid 
>tie inverter from the grid.
>
>I've played with the voltage set points, but the charge voltage on 
>the Magnum would be too low for good battery maintenance.  If these 
>were liquid electrolyte batteries, I'd crank up the voltage on the 
>relay driver.  Since they are AGM batteries, it doesn't seem like a 
>good idea to do that.
>
>The work around for this at present is to;
>    * Charge batteries at night in the winter
>    * No problem is expected in the summer
>The batteries are in an insulated box in a shed connected to the 
>house. The inside of the battery box has a screened hole that is 
>supposed to allow heated air into the box.  This vent doesn't keep 
>the batteries warm enough to prevent the problem.
>
>Is there a temperature sensitive, voltage controlled relay or diver 
>available?  Has anyone used a temperature bulb with the relay driver 
>in a way that could solve this problem? Has anyone else come up 
>against this issue, and if so, what was your solution?
>
>Thanks,
>
>Drake
>
>
>Drake Chamberlin
>Athens Electric LLC
>OH License 44810
>CO License 3773
>NABCEP Certified Solar PV Installer
>740-448-7328
><http://athens-electric.com/>http://athens-electric.com/
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: 
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: 
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130308/bf0e9544/attachment.htm>


More information about the RE-Wrenches mailing list