Thank you to all who responded to this post. <br><br>
Larry, that sounds like a great potential solution. That will put the
frequency shift in line with where the battery cutoff voltage needs to
be. The frequency shift happens 2 volts above the absorption charge set
point. My only issue with the solution is the 1 1/2 hour round trip to
the site (it could be worse).&nbsp; Maybe Concorde can give me
information that will allow me to set up the charge parameters without
having to tweak.&nbsp; <br><br>
Allan, dump loads are a great way to go, for sure. The tech I spoke to at
Magnum recommended the relay as a fail safe for the frequency
shift.&nbsp; When the issue of the inverter frequency shifting at 2 volts
above the absorption charge set point came up, the relay became the
primary protective device for the AGM batteries.  <br><br>
We didn't use diversion loads since this is a backup system, and will
probably only operate a few days per year.&nbsp; The inverter should
maintain the batteries rather than the solar. We used the Morningstar
relay driver, in part, to allow dump loads to be added if desired.&nbsp;
<br><br>
Another solution was offered by APRS World, LLC.&nbsp; They likely can
build products that would trigger relays using the temperature
compensated data from the Magnum Network.&nbsp; <br><br>
It would sure simplify life it Magnum could add an axillary relay.&nbsp;
Would that require putting the inverter, or entire line of inverters,
back into UL for re-approval? <br><br>
Drake <br><br>
&nbsp;<br>
At 05:36 PM 3/7/2013, you wrote:<br>
<blockquote type=cite class=cite cite="">Meant to say, &quot;You should
tweak #3 &amp; #4 above...&quot;<br><br>
<br>
Drake,<br><br>
Charging an AGM battery does not have to occur at the maximum charge
voltage allowable; you can charge at a lower voltage for longer periods
of time and still achieve 100% SoC. Since you have grid power to work
with, slow down the charge cycle.<br><br>
Assuming you have a late model ME-RC and version 5 or higher inverter,
you can custom program the charge voltages. Here's what I would do: 
<ol>
<li>Go to Custom settings for battery type (setup menu 04).
<li>Set the Absorb voltage for 26.8.
<li>Set the Float for 26.4
<li>Set the absorb time to 8 hours
<li>Be sure the charge rate( setup menu 05) is 100%.
</ol><br>
Near the end of the absorb charge cycle, measure the current going into
the battery. If it is less than 0.2 amps/100AH capacity, the bank is
full. You should #3 &amp; #4 above until it works out for the low temp.
comp. and charge time but it should work well.<br><br>
If you are concerned about this lower voltage, set up a periodic equalize
charge to 28.8.<br><br>
Larry Crutcher<br>
Starlight Solar Power Systems<br><br>
<br><br>
<br><br>
On Mar 7, 2013, at 3:00 PM, Drake wrote:<br><br>
Hello Wrenches,<br><br>
I had an unexpected glitch in AC coupling a Magnum 4024 PAE
inverter.&nbsp; The system utilizes AGM batteries, which (according to
Concorde tech support) have a very strict upper voltage limit.<br><br>
The relay used to stop the current input from the direct grid tie
inverter, when battery voltage is high, is controlled by a Morningstar
Relay Driver.&nbsp; The relay driver is set to shut off the charge at
28.8 volts.<br><br>
The charger on the Magnum is set to charge the batteries to&nbsp; 28.6
volts.&nbsp; <br><br>
The plan was to be able to charge batteries from the Magnum without
tripping the AC connection between the grid tie inverter to the
grid.&nbsp; The Magnum should charge to 28.6 volts, 0.2 volts below the
relay driver's programmed trigger point. <br><br>
There is one catch to using this approach. The Magnum inverter has a
remote temperature sensor in the battery bank. The relay driver is not
temperature corrected. Therefore, when the batteries are cold, the
charging voltage goes up in the Magnum.&nbsp; This higher voltage trips
the relay controlled by the driver, and disconnects the grid tie inverter
from the grid.&nbsp; <br><br>
I've played with the voltage set points, but the charge voltage on the
Magnum would be too low for good battery maintenance.&nbsp; If these were
liquid electrolyte batteries, I'd crank up the voltage on the relay
driver.&nbsp; Since they are AGM batteries, it doesn't seem like a good
idea to do that. <br><br>
The work around for this at present is to; 
<ul>
<li>Charge batteries at night in the winter 
<li>No problem is expected in the summer 
</ul>The batteries are in an insulated box in a shed connected to the
house. The inside of the battery box has a screened hole that is supposed
to allow heated air into the box.&nbsp; This vent doesn't keep the
batteries warm enough to prevent the problem. <br><br>
Is there a temperature sensitive, voltage controlled relay or diver
available?&nbsp; Has anyone used a temperature bulb with the relay driver
in a way that could solve this problem? Has anyone else come up against
this issue, and if so, what was your solution?<br><br>
Thanks,<br><br>
Drake <br><br>
<br>
<a name="_MailAutoSig"></a>Drake Chamberlin<br>
<i>Athens Electric LLC<br>
OH License 44810<br>
CO License 3773<br>
NABCEP Certified Solar PV Installer<br>
740-448-7328<br>
</i><a href="http://athens-electric.com/">http://athens-electric.com/</a>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a><br><br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a><br><br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Change email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote></body>
</html>