Ross,
I couldn't agree more...the Midnite SPDs are far superior to those cans
of silica sand that
many of us have been installing for years. The video of the comparison
test between the
Delta and the SPD arrestor is well worth watching.
Not to mention the colorful MOVs and pretty light inside ;-)
Roy Butler
NABCEP Certified Small Wind Installer®
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747 www.four-winds-energy.com
Join us at the 9th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 18 and 19, 2013 in Stevens Point, Wisconsin
www.smallwindconference.com
Although no trees were killed in the sending of this message,
a large number of electrons were terribly inconvenienced.
On 8/18/2012 2:12 PM, Ross Taylor wrote:
> Surge protection: for the price and quality and function, it's almost impossible to beat the Midnight Solar SPDs.
> ___________________________________
> Ross Taylor - International Training Manager
> Southwest Windpower
>
> (Sent "mobily" so please forgive brevity or typos)
>
> "re-wrenches-request at lists.re-wrenches.org" <re-wrenches-request at lists.re-wrenches.org> wrote:
>
>
> Send RE-wrenches mailing list submissions to
> re-wrenches at lists.re-wrenches.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
> or, via email, send a message with subject or body 'help' to
> re-wrenches-request at lists.re-wrenches.org
>
> You can reach the person managing the list at
> re-wrenches-owner at lists.re-wrenches.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of RE-wrenches digest..."
>
>
> When responding to posts within the Digest, be sure to restore the Subject: line to the original, and please edit out any extraneous lines from the quoted message.
>
>
> Today's Topics:
>
> 1. Re: Best practices for comp shingle flashing? (August Goers)
> 2. Surge Protection- PV (Keith Cronin)
> 3. Booster pump (Nathan Stumpff)
> 4. Heart Interface Inverter (mac Lewis)
> 5. Re: Heart Interface Inverter (Chris Mason)
> 6. Re: Heart Interface Inverter (bob ellison)
> 7. Re: Heart Interface Inverter (Jay Peltz)
> 8. Combating requests for itemized PV pricing (Jason Szumlanski)
> 9. Re: Combating requests for itemized PV pricing (Allan Sindelar)
>
>
> ----------------------------------------------------------------------
>
> Message: 1
> Date: Fri, 17 Aug 2012 11:48:14 -0700
> From: August Goers <august at luminalt.com>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Best practices for comp shingle flashing?
> Message-ID: <e1fd9211d08550b141810da0059d23bf at mail.gmail.com>
> Content-Type: text/plain; charset="iso-8859-1"
>
> Hi Eric,
>
>
>
> We've used TTi, EcoFasten, and Quick Mount. I like Quick Mount the best but
> they are a bit pricy so we've been using Eco Fasten for the majority of our
> work over the last year. If anything, I've found that TTi requires more
> labor and is more likely to require shingle cutting plus I'm gun-shy about
> their material quality. That said, the majority of our standard comp
> shingle mounts require no shingle cutting (although you might have to
> remove a nail or two) with Quick Mount or Eco Fasten. You just slide them
> up under the shingles as pictured in this video:
>
>
>
> http://www.quickmountpv.com/training/videos/classic-comp-install.html
>
>
>
> Maybe you have a different kind of comp in your neck of the woods? If
> you're really worried about it you can always take a sample out and see if
> you can slide it under the shingles without any cutting. It just might work.
>
>
>
> Good luck.
>
>
>
> Best, August
>
>
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *SunHarvest
> *Sent:* Wednesday, August 15, 2012 4:22 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Best practices for comp shingle flashing?
>
>
>
> Thanks guys. Talked with TTi and mentioned Mr. Miller's experience with
> rust. They said they got a lot of feedback about this problem on their 1st
> generation line and have since corrected the issue. I'll remain
> cautious...thanks Willy.
>
>
>
> TTi, DPW, EcoFasten, and Quick-mount all seem to have the same issue of
> lacking versatility in height adjustment. Anyway, going to check out a
> sample from TTi. DPW and EcoFasten look like they still require cutting of
> both flash base and comp courses. I'm trying to avoid cutting anything as I
> want to avoid disturbing original flashing and original roofing material.
>
>
>
> Thanks for all your input!!
>
>
>
> Eric Stikes
> SunHarvest Solar
> A Sustainable Energy Group Partner
> +1 (530) 798 - 3738
> www.harvesthesun.com
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120817/59552db0/attachment.html>
>
> ------------------------------
>
> Message: 2
> Date: Fri, 17 Aug 2012 13:52:31 -0700 (PDT)
> From: Keith Cronin <electrichi01 at yahoo.com>
> To: RE-Wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] Surge Protection- PV
> Message-ID:
> <1345236751.89820.YahooMailNeo at web113414.mail.gq1.yahoo.com>
> Content-Type: text/plain; charset="iso-8859-1"
>
> Hi folks
>
> What kinds of products are you using for residential and commercial surge protection for your PV systems?
>
> Have a few clients that have been asking.
>
> Is it at the service, using products like this:
> http://www.cooperindustries.com/content/public/en/bussmann/electrical/products/surge_protectiondevice/photovoltaic_spd.videos.html
>
>
> I always wonder what it protects and the fine print in the event of a lightning storm to someone hitting a pole on the street and sending the surge back into the property.
> ?
> Aloha,
>
>
> Keith
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120817/b3f7b32d/attachment-0001.htm>
>
> ------------------------------
>
> Message: 3
> Date: Fri, 17 Aug 2012 15:22:10 -0800
> From: Nathan Stumpff <Nathan at arcticsun-llc.com>
> To: "re-wrenches at lists.re-wrenches.org"
> <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] Booster pump
> Message-ID:
> <F0293D22AADF0B4BB93164A4BF88390F449550DB6D at REINA-SERVER.reina.local>
> Content-Type: text/plain; charset="us-ascii"
>
> Thermal wrenches,
>
> When plumbing a booster pump in series for a solar drainback system, should the booster pump go ahead of or behind the main circulator?
>
> Cheers,
> -Nathan
>
> --
> Nathan J. Stumpff - Arctic Sun, LLC
> NABCEP Certified PV Installer #091209-175
> NABCEP Certified Solar Heating Installer #032412-14
> nathan at arcticsun-llc.com<mailto:nathan at arcticsun-llc.com>
> Office: 907/457-1297
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120817/9fb2b1bb/attachment-0001.htm>
>
> ------------------------------
>
> Message: 4
> Date: Fri, 17 Aug 2012 20:24:34 -0600
> From: mac Lewis <maclewis1 at gmail.com>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] Heart Interface Inverter
> Message-ID:
> <CAOABG49x1m0muMY_wyyHfHE1anQRDmCS8zKTLDnJYDE9r0zmZA at mail.gmail.com>
> Content-Type: text/plain; charset="iso-8859-1"
>
> Hello Wrenches,
>
> AC charging system specs
> Onan Marquis Gold 5500 LP Model 5.5HGJAB119D generator
> Heart Interface Freedom 20 Model Inverter Charger (120VAC, 100A charger,
> 12VDC)
>
> I have a new customer who has a used Onan RV generator (as specified
> above), working with a Heart Inverter charger (specified above). When the
> generator is started, the Heart inverter kicks on and starts to charge,
> after about 3 seconds it kicks off, then on, then off and repeats. The
> voltage and frequency of the generator output look good. 120V L-N and 60-62
> Hz no load. The Heart just doesn't seem to like it after it kicks on the
> charger. (Sorry, no scopemeter available)
>
> What is very interesting is that on the other pole of a transfer switch
> connected to the AC input, is a fairly inexpensive gas generator, pull
> start, on wheels etc. This puts out 108VAC at 59-60Hz. When connected to
> this generator the Heart immediately latches in and will continue charging
> flawlessly at 100ADC. For whatever reason, the Heart, doesn't like the
> voltage waveform of the Onan generator. The Fluke 87 multimeter that I was
> using to test, was catching some type of transient (frequency reading would
> shoot up to 70-100Hz) when the Heart would latch into the Onan. Other that
> that with my simple tools I could see no real difference between these
> generators, other that the 108VAC of the gas generator.
>
> Any ideas, or known compatibility issues with this equipment?
>
> Thanks
>
> --
>
>
>
> Mac Lewis
>
> *
>
> "Yo solo s? que no s? nada." -S?crates
> *
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120817/e7fb717a/attachment-0001.htm>
>
> ------------------------------
>
> Message: 5
> Date: Sat, 18 Aug 2012 07:25:41 -0400
> From: Chris Mason <cometenergysystems at gmail.com>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Heart Interface Inverter
> Message-ID:
> <CAG6C1qkQKtcB5TCMaEQk3ddQcQMJWUjX7-kigKdN=nHJB65X_Q at mail.gmail.com>
> Content-Type: text/plain; charset="iso-8859-1"
>
> For what it's worth, the Fluke is known to mistake harmonics for base
> frequency. I would look to borrow for a scope or at least use a cheaper
> meter that can accurately report the frequency. Try slowing the generator
> to 59 Hz to see if the inverter likes it better.
>
>
> On Fri, Aug 17, 2012 at 10:24 PM, mac Lewis <maclewis1 at gmail.com> wrote:
>
>> Hello Wrenches,
>>
>> AC charging system specs
>> Onan Marquis Gold 5500 LP Model 5.5HGJAB119D generator
>> Heart Interface Freedom 20 Model Inverter Charger (120VAC, 100A charger,
>> 12VDC)
>>
>> I have a new customer who has a used Onan RV generator (as specified
>> above), working with a Heart Inverter charger (specified above). When the
>> generator is started, the Heart inverter kicks on and starts to charge,
>> after about 3 seconds it kicks off, then on, then off and repeats. The
>> voltage and frequency of the generator output look good. 120V L-N and 60-62
>> Hz no load. The Heart just doesn't seem to like it after it kicks on the
>> charger. (Sorry, no scopemeter available)
>>
>> What is very interesting is that on the other pole of a transfer switch
>> connected to the AC input, is a fairly inexpensive gas generator, pull
>> start, on wheels etc. This puts out 108VAC at 59-60Hz. When connected to
>> this generator the Heart immediately latches in and will continue charging
>> flawlessly at 100ADC. For whatever reason, the Heart, doesn't like the
>> voltage waveform of the Onan generator. The Fluke 87 multimeter that I was
>> using to test, was catching some type of transient (frequency reading would
>> shoot up to 70-100Hz) when the Heart would latch into the Onan. Other that
>> that with my simple tools I could see no real difference between these
>> generators, other that the 108VAC of the gas generator.
>>
>> Any ideas, or known compatibility issues with this equipment?
>>
>> Thanks
>>
>> --
>>
>>
>>
>> Mac Lewis
>>
>> *
>>
>> "Yo solo s? que no s? nada." -S?crates
>> *
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> --
> Chris Mason
> President, Comet Systems Ltd
> www.cometenergysystems.com
> Cell: 264.235.5670
> Skype: netconcepts
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120818/d81eab38/attachment-0001.htm>
>
> ------------------------------
>
> Message: 6
> Date: Sat, 18 Aug 2012 10:07:33 -0400
> From: "bob ellison" <reellison at gmail.com>
> To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Heart Interface Inverter
> Message-ID: <006b01cd7d4b$175ea430$461bec90$@com>
> Content-Type: text/plain; charset="iso-8859-1"
>
> Try putting a load on the generator (like a 1500 watt hair dryer) before the
> Heart kicks on then once it transfers to the loads and starts charging, shut
> it off.
>
> It might be finding the voltage or frequency to high for it?s liking.
>
> Plug it directly into the generator of somewhere before the inverter to get
> gen power.
>
>
>
> Bob Ellison
>
>
>
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Chris Mason
> Sent: Saturday, August 18, 2012 7:26 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Heart Interface Inverter
>
>
>
> For what it's worth, the Fluke is known to mistake harmonics for base
> frequency. I would look to borrow for a scope or at least use a cheaper
> meter that can accurately report the frequency. Try slowing the generator to
> 59 Hz to see if the inverter likes it better.
>
>
>
> On Fri, Aug 17, 2012 at 10:24 PM, mac Lewis <maclewis1 at gmail.com> wrote:
>
> Hello Wrenches,
>
>
>
> AC charging system specs
>
> Onan Marquis Gold 5500 LP Model 5.5HGJAB119D generator
>
> Heart Interface Freedom 20 Model Inverter Charger (120VAC, 100A charger,
> 12VDC)
>
>
>
> I have a new customer who has a used Onan RV generator (as specified above),
> working with a Heart Inverter charger (specified above). When the generator
> is started, the Heart inverter kicks on and starts to charge, after about 3
> seconds it kicks off, then on, then off and repeats. The voltage and
> frequency of the generator output look good. 120V L-N and 60-62 Hz no load.
> The Heart just doesn't seem to like it after it kicks on the charger.
> (Sorry, no scopemeter available)
>
>
>
> What is very interesting is that on the other pole of a transfer switch
> connected to the AC input, is a fairly inexpensive gas generator, pull
> start, on wheels etc. This puts out 108VAC at 59-60Hz. When connected to
> this generator the Heart immediately latches in and will continue charging
> flawlessly at 100ADC. For whatever reason, the Heart, doesn't like the
> voltage waveform of the Onan generator. The Fluke 87 multimeter that I was
> using to test, was catching some type of transient (frequency reading would
> shoot up to 70-100Hz) when the Heart would latch into the Onan. Other that
> that with my simple tools I could see no real difference between these
> generators, other that the 108VAC of the gas generator.
>
>
>
> Any ideas, or known compatibility issues with this equipment?
>
>
>
> Thanks
>
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo s? que no s? nada." -S?crates
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>
>
>
>
>
>
> --
> Chris Mason
>
> President, Comet Systems Ltd
>
> www.cometenergysystems.com
>
> Cell: 264.235.5670
>
> Skype: netconcepts
>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120818/9c100462/attachment-0001.htm>
>
> ------------------------------
>
> Message: 7
> Date: Sat, 18 Aug 2012 07:23:40 -0700
> From: Jay Peltz <jay at asis.com>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Heart Interface Inverter
> Message-ID: <ABBFDF4E-B567-4A75-8A52-B527EBC8D615 at asis.com>
> Content-Type: text/plain; charset="utf-8"
>
> Hi folks
> You might also check peak volts. If memory serves correctly those older inverters charged off peak volts not RMS.
>
> Jay
> Peltz power
>
> Sent from my iPhone
>
> On Aug 18, 2012, at 7:07 AM, "bob ellison" <reellison at gmail.com> wrote:
>
>> Try putting a load on the generator (like a 1500 watt hair dryer) before the Heart kicks on then once it transfers to the loads and starts charging, shut it off.
>> It might be finding the voltage or frequency to high for it?s liking.
>> Plug it directly into the generator of somewhere before the inverter to get gen power.
>>
>> Bob Ellison
>>
>> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Chris Mason
>> Sent: Saturday, August 18, 2012 7:26 AM
>> To: RE-wrenches
>> Subject: Re: [RE-wrenches] Heart Interface Inverter
>>
>> For what it's worth, the Fluke is known to mistake harmonics for base frequency. I would look to borrow for a scope or at least use a cheaper meter that can accurately report the frequency. Try slowing the generator to 59 Hz to see if the inverter likes it better.
>>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120818/675c679b/attachment-0001.htm>
>
> ------------------------------
>
> Message: 8
> Date: Sat, 18 Aug 2012 12:18:54 -0400
> From: Jason Szumlanski <jason at fafcosolar.com>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] Combating requests for itemized PV pricing
> Message-ID:
> <CAJJtG3ozGzQwZgRBYpmRJYUWBS0WOuxDQ7jV4TRosFKyi2XAwQ at mail.gmail.com>
> Content-Type: text/plain; charset="iso-8859-1"
>
> We are getting more and more people calling that want to provide their own
> equipment and have us install it. It's frustrating, because usually they
> are looking at prices for materials that either I would not consider
> selling, or would not meet the mounting requirements of the Florida
> Building Code. Of course, they do not understand and consider all of the
> other costs.
>
> In addition, lots of people are looking for a breakdown of prices (down to
> the line item - nuts and bolts). I generally refuse to provide it because
> it inevitably leads to the response "I can get that module/inverter online
> cheaper." The "I need to make money" response leads to "yeah, but you must
> be getting better prices than I see online" argument. And so on, and so
> on... I'm sure you've heard it...
>
> I've resorted recently to just providing a percentage breakdown,
> stating that the price is roughly 25% each:
>
> - PV Modules
> - Inverters and Electrical
> - Mounting System
> - Design/Engineering, Permitting, Labor, Overhead, and Profit
>
> Any other tips out there to answer the request for line item details?
>
> Jason Szumlanski
> Fafco Solar
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120818/9ed60134/attachment-0001.htm>
>
> ------------------------------
>
> Message: 9
> Date: Sat, 18 Aug 2012 11:17:36 -0600
> From: Allan Sindelar <allan at positiveenergysolar.com>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Combating requests for itemized PV pricing
> Message-ID: <502FCE30.2080804 at positiveenergysolar.com>
> Content-Type: text/plain; charset="us-ascii"
>
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120818/1b0f2d96/attachment-0001.htm>
>
> ------------------------------
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> End of RE-wrenches Digest, Vol 5, Issue 256
> *******************************************
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
More information about the RE-Wrenches
mailing list