[RE-wrenches] Landing into a sub-panel without a mainservicepanel, just a main switch

Jason Szumlanski Jason at fafcosolar.com
Fri Dec 23 13:56:13 EST 2011


If you are interested in this discussion, you may want to take a look at “Quality Assurance: NEC Section 705.12 and Utility Interconnections: in SolarPro Magazine, Dec/Jan 2012, Issue 5.1. The 2011 NEC does not clarify supply side connections much.

 

One frustrating issue I ran into recently was the *location* of PV service disconnects. The AHJ insisted that the PV AC Disco needed to be co-located with the main service disconnect (i.e. inside the house at the MDP). I argued that it could be outside next to the meter as long as the appropriate labels were applied. I lost that battle.

 

Jason Szumlanski

Fafco Solar

 

 

From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of JRQ
Sent: Friday, December 23, 2011 11:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Landing into a sub-panel without a mainservicepanel, just a main switch

 

I've been working in San Diego mostly in the last few years and the utility, SDG&E, won't let anyone do line- or load- side taps unless they can show documentation that the enclosure is specifically rated for such a tap, or if they pay for an EE to sign off on it. So a line-side tap can create equal compliance problems, depending on the jurisdiction.

 

Jeffrey Quackenbush

 