[RE-wrenches] Landing into a sub-panel without a main servicepanel, just a main switch
JRQ
quackkcauq at yahoo.com
Fri Dec 23 11:27:30 EST 2011
I've been working in San Diego mostly in the last few years and the utility, SDG&E, won't let anyone do line- or load- side taps unless they can show documentation that the enclosure is specifically rated for such a tap, or if they pay for an EE to sign off on it. So a line-side tap can create equal compliance problems, depending on the jurisdiction.
Jeffrey Quackenbush
________________________________
From: Jason Szumlanski <Jason at fafcosolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Friday, December 23, 2011 7:30 PM
Subject: Re: [RE-wrenches] Landing into a sub-panel without a main servicepanel, just a main switch
We have avoided any load side code issues by doing supply side taps on older buildings. The AHJ typically turns a blind eye to the load side issues if we use this interconnection method. That is not to say that you shouldn’t strongly encourage the owner to address the load side deficiencies or code violations, if any. Nonetheless, adding solar to the supply side of the main disconnect would not exacerbate any existing problems on the load side.
Jason Szumlanski
Fafco Solar
From:re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of JRQ
Sent: Friday, December 23, 2011 3:51 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Landing into a sub-panel without a main servicepanel, just a main switch
Yes, if there is a distribution block and several subpanels are fed from the same point downline from the main disconnect, then what I'm describing would not be applicable. The other subpanels function as loads with respect to the distribution block. The same if there are any taps on the load side of the main disconnect.
We need to see a wiring diagram for how these subpanels are connected together to give a definitive answer.
Jeffrey Quackenbush.
________________________________
From:Richard L Ratico <Richard.L.Ratico at VALLEY.NET>
To: re-wrenches at lists.re-wrenches.org
Sent: Friday, December 23, 2011 9:43 AM
Subject: Re: [RE-wrenches] Landing into a sub-panel without a main service panel, just a main switch
Jeffrey,
On the load side of the Fused 200 Amp Service Disconnect there is a splice or
splices or distribution block in the conductors which feed the 5 subpanels. It
seems quite possible that one or more of those conductors or the distribution
block could see the sum of the current from the grid and the current from the
solar. A combination of loads in the 4 subpanels, other than the one backfed by
the solar breaker, could overload the conductor or part of that conductor
carrying that combined current, without necessarily blowing a main fuse or any
of the breakers. The devil is in the details, in this case the size of the
conductors and the way they are utilized.
Ray has a point. It is possible there are existing code violations. These should
be corrected in a manner which facilitates inclusion of the solar.
Dick Ratico
Solarwind Electric
--- You wrote:
The flow of electricity isn't two-way traffic along a conductor. If there are no
loads on the conductor between the main system disconnect and the main breaker
of a subpanel, in this scenario, there can only be up to 200 A coming from the
utility OR up to 60 A coming from the solar system backfed through the subpanel.
The intent of limiting the solar system size plus the utility source to 120%, or
even 100%, of a bus or conductor rating is when that bus or conductor can
potentially see current from both sources simultaneously, it could overheat if
these sources exceed the bus or conductor rating. That's not physically possible
unless there is a load in between both sources.
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20111223/81395bc1/attachment.htm>
More information about the RE-Wrenches
mailing list