Lumeta dealer has been sending links for unlisted wire management systems,
nothing from Lumeta itself. Cooper B-Line EnviroShield is listed and is an
easier drop in raceway but very expensive.

On Tue, Sep 6, 2011 at 4:02 PM, Mark Frye <markf at berkeleysolar.com> wrote:

> **
> The idea of "within the array" goes to the idea that the conductors will be
> located on the underside of an array of traditional framed moduled and will
> be afforded a modicum of protection from physical damage by the module
> itself.
>
> So the issue is one of physical protection of the conductors. That is what
> tha AJH should be looking to. If he has cold feet about approving a
> non-standard method using un-listed componets based on local conditions,
> then he is understandably going to ask for a solution utilizing listed
> materials and standard methods.
>
> What kind of support are you getting from Lumeta around this?
>
> Mark Frye
> Berkeley Solar Electric Systems
> 303 Redbud Way
> Nevada City,  CA 95959
> (530) 401-8024
> *www.berkeleysolar.com* <http://www.berkeleysolar.com/>
>
>
>  ------------------------------
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *
> wirewiz at gmail.com
> *Sent:* Tuesday, September 06, 2011 12:44 PM
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* [RE-wrenches] 690.31(B) "within the photovoltaic array"
>
> Wrenches,
>
> I am installing Lumeta peel and stick modules (similar to laminates) on a
> flat EPDM roof. No racking. NEC2008 690.31(B) says single conductor cable
> listed and labeled as PV wire shall be permitted in exposed outdoor
> locations..."within the array". 690.2 defines array as a mechanically
> integrated assembly of modules or panels within a support structure...to
> form a direct-current power producing unit. With the Lumeta's there is no
> support structure. If you look at the diagram in the NEC 2008 (page 70-576)
> it shows a box around the modules or panels and labels that box as the
> "Array or photovoltaic power source".
>
> My AHJ was at first not sure but then told me I had to install all the PV
> wire in a listed raceway because the interconnects between the Lumeta's were
> not within the array. But if you draw a box around all the Lumeta's it would
> look like the array diagram that I referred to above.
>
> Because of my roof layout, it would be much easier to install an unlisted
> wire management system within the array rather than conduit which I will do
> but in reading the NEC it just wasn't clear to me what "within the array"
> means.
>
> Any thoughts would be appreciated.
>
> Thank you.
>
> Larry Liesner
> Design and Installations
> Elektron Solar, LLC
> 16 Ketchum St.
> Westport, CT 06880
> 203-557-3127 (office)
> 203-644-2404 (cell)
> 203-549-0977 (fax)
> wirewiz at gmail.com
> NABCEP Certified PV Installer (# 032611-184)
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Larry Liesner
Design and Installations
Elektron Solar, LLC
49 Richmondville Ave Suite 107
Westport, CT 06880
203-557-3127 (office)
203-644-2404 (cell)
203-549-0977 (fax)
wirewiz at gmail.com
NABCEP Certified PV Installer (# 032611-184)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110906/05c5ffed/attachment-0001.htm>


More information about the RE-Wrenches mailing list