Lumeta dealer has been sending links for unlisted wire management systems, nothing from Lumeta itself. Cooper B-Line EnviroShield is listed and is an easier drop in raceway but very expensive.<br><br><div class="gmail_quote">
On Tue, Sep 6, 2011 at 4:02 PM, Mark Frye <span dir="ltr">&lt;<a href="mailto:markf@berkeleysolar.com">markf@berkeleysolar.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<u></u>



<div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial" size="2">The idea of &quot;within the array&quot; goes to the idea that the 
conductors will be located on the underside of an array oftraditional 
framed moduled and will be afforded a modicum of protection from physical damage 
by the module itself.</font></span></div>
<div><font color="#0000ff" face="Arial" size="2"></font></div>
<div><span><font color="#0000ff" face="Arial" size="2">So the 
issue is one of physical protection of the conductors. That is what tha AJH 
should be looking to. If he has cold feet about approving a non-standard method 
using un-listedcomponets based on local conditions, then he is 
understandably going to ask for a solution utilizing listed materials and 
standard methods.</font></span></div>
<div><span><font color="#0000ff" face="Arial" size="2"></font></span></div>
<div><span><font color="#0000ff" face="Arial" size="2">What 
kind of support are you getting from Lumeta around this?</font></span></div>
<div><span><font color="#0000ff" face="Arial" size="2"></font></span><br><span lang="en-us"><font face="Arial" size="2">Mark 
Frye</font></span> <br><span lang="en-us"><font face="Arial" size="2">Berkeley Solar 
Electric Systems</font></span> <br><span lang="en-us"><font face="Arial" size="2">303 
Redbud Way</font></span> <br><span lang="en-us"><font face="Arial" size="2">Nevada 
City, CA 95959</font></span> <br><span lang="en-us"><font face="Arial" size="2"><a href="tel:%28530%29%20401-8024" value="+15304018024" target="_blank">(530) 401-8024</a></font></span> <br><span lang="en-us"></span><a href="http://www.berkeleysolar.com/" target="_blank"><span lang="en-us"><u><font color="#0000ff" face="Arial" size="2">www.berkeleysolar.com</font></u></span></a><span lang="en-us"><font face="Arial" size="2"></font></span> </div>

<div></div><br>
<div dir="ltr" align="left" lang="en-us">
<hr>
<font face="Tahoma" size="2"><b>From:</b> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a> 
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of 
</b><a href="mailto:wirewiz@gmail.com" target="_blank">wirewiz@gmail.com</a><br><b>Sent:</b> Tuesday, September 06, 2011 12:44 
PM<br><b>To:</b> <a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a><br><b>Subject:</b> 
[RE-wrenches] 690.31(B) &quot;within the photovoltaic array&quot;<br></font><br></div><div><div></div><div class="h5">
<div></div>Wrenches,<br><br>I am installing Lumeta peel and stick modules 
(similar to laminates) on a flat EPDM roof. No racking. NEC2008 690.31(B) says 
single conductor cable listed and labeled as PV wire shall be permitted in 
exposed outdoor locations...&quot;within the array&quot;. 690.2 defines array as a 
mechanically integrated assembly of modules or panels within a support 
structure...to form a direct-current power producing unit. With the Lumeta&#39;s 
there is no support structure. If you look at the diagram in the NEC 2008 (page 
70-576) it shows a box around the modules or panels and labels that box as the 
&quot;Array or photovoltaic power source&quot;. <br><br>My AHJ was at first not sure but 
then told me I had to install all the PV wire in a listed raceway because the 
interconnects between the Lumeta&#39;s were not within the array. But if you draw a 
box around all the Lumeta&#39;s it would look like the array diagram that I referred 
to above.<br><br>Because of my roof layout, it would be much easier to install 
an unlisted wire management system within the array rather than conduit which I 
will do but in reading the NEC it just wasn&#39;t clear to me what &quot;within the 
array&quot; means.<br><br clear="all">Any thoughts would be appreciated.<br><br>Thank 
you.<br><br>Larry Liesner<br>Design and Installations<br>Elektron Solar, 
LLC<br>16 Ketchum St.<br>Westport, CT 06880<br><a href="tel:203-557-3127" value="+12035573127" target="_blank">203-557-3127</a> 
(office)<br><a href="tel:203-644-2404" value="+12036442404" target="_blank">203-644-2404</a> (cell)<br><a href="tel:203-549-0977" value="+12035490977" target="_blank">203-549-0977</a> (fax)<br><a href="mailto:wirewiz@gmail.com" target="_blank">wirewiz@gmail.com</a><br>
NABCEP 
Certified PV Installer (# 032611-184)<br><br></div></div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Larry Liesner<br>Design and Installations<br>Elektron Solar, LLC<br>49 Richmondville Ave Suite 107<br>Westport, CT 06880<br>203-557-3127 (office)<br>203-644-2404 (cell)<br>
203-549-0977 (fax)<br><a href="mailto:wirewiz@gmail.com" target="_blank">wirewiz@gmail.com</a><br>NABCEP Certified PV Installer (# 032611-184)<br><br>