I have REC 215 on Enphase 190. I see a lot of clipping. Every sunny day in the
winter and spring. I have some data but it is only 15 minute, and I see this
happen even in june.
________________________________
From: Drake <drake.chamberlin at redwoodalliance.org>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Thu, January 20, 2011 8:23:55 AM
Subject: Re: [RE-wrenches] Inverter oversizing
On a couple of Enphase systems I monitor regularly, the modules are oversized
compared to the inverters. One system has Sharp 224 W modules and M-190s
(capable of producing 199 W). The array is a ground mount at a 30 degree tilt
at 39+ degrees latitude.
When the system was new in the autumn, I noticed two days of some clipping.
Since then, none. In the summer, when the sun angle is better, the heat will
keep the wattage down so clipping will very seldom occur. The modules will not
be close to STC, so the inverters should not be pushed to their maximum.
The same is true of string inverters. Since real power of the modules in
generally significantly below the nameplate, inverters will generally not run at
maximum power. When we take in all the factors affecting the actual array
power, I think that 120% over sizing from nameplate wattage is generally safe.
Drake
At 09:14 PM 1/19/2011, you wrote:
David,
>
>Thanks for sharing that paper. The labeling the graphs for the 10-second and
>1-minute data in Freiburg appears to be reversed - the one minute averaging
>seems to have more data in all of the bins above 1000 W/sq m. Basically, these
>graphs show that irradiance observations above 1100 watts per square meter are
>fleeting and disappear in hourly averages. Such occurrences are also masked to
>a small extent by 1-minute averages.
>
>Kent Osterberg
>Blue Mountain Solar, Inc.
>
>
>
>David Brearley wrote:
>
>This reminds me of a scholarly article I came across about a year ago while
>doing some research. Here’s a link to it if anyone is interested:
>>
>>www.lepten.ufsc.br/publicacoes/solar/eventos/2005/PSC/burger_ruther.pdf
>>
>>David Brearley, Senior Technical Editor
>>SolarPro magazine
>>NABCEP Certified PV Installer ™
>>david.brearley at solarprofessional.com
>>Direct: 541.261.6545
>>
>>On 1/19/11 12:29 PM, "Bill Brooks" <billbrooks7 at yahoo.com> wrote:
>>
>>
>>Kent,
>>
>>
>>
>>
>>How often were your data records? To capture edge of cloud effects, you need
>>one-second data. Not many people gather that fast or that much data on
>>inverters. I don’t think there is that much energy in these spikes, but they are
>>real and make some difference. 15-minute average data will completely wash out
>>this data.
>>
>>
>>
>>This is also a deficiency in modeling software since most models are using
>>hourly data.
>>
>>
>>
>>Bill.
>>
>>
>>
>>From: re-wrenches-bounces at lists.re-wrenches.org
>>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent Osterberg
>>
>>
>>
>>Sent: Tuesday, January 18, 2011 1:18 PM
>>
>>To: Wrenches; Marco Mangelsdorf
>>
>>Subject: [RE-wrenches] Inverter oversizing
>>
>>Attached is a graph that I produced to document the effect of various ratios
>>between the PV array size and the inverter size. I extracted output power data
>>for a 1020-watt system located in NE Oregon that is on the Sunny Portal
>><http://www.sunnyportal.com/Templates/PublicPageOverview.aspx?page=85820a73-a347-48fb-b8d1-92e5f9b78ab3&plant=608681a7-ef60-4edb-84ff-07110db0ab6a&splang=en-US
>> > . The data are publicly accessible so feel free to run your own analysis.
>>Better yet, analyze the data for a system near you.
>>
>>
>>
>>Using 2009 data, I looked at how much energy would have been lost if the output
>>was clipped at 800W, 810W, .... 1020W. I used 2009 data because there was a
>>period in 2010 when the Sunny Webbox didn't have internet access. At 800 watts,
>>power clipping would have happened on about 25% of the days. Yet the energy
>>that would have been lost was only 0.38% of the annual total.
>>
>>
>>
>>The results shown on this graph aren't universal, results would be a little
>>different in 2010, it would be different in some other climate, it would have
>>been different at another elevation, it would be different with a different
>>array angle, ..., and the module tolerance and inverter efficiency also effect
>>the results. Modules in this system are Suntech 170-watt +/-3%. The inverter
>>is Sunnyboy 1800 that should be operating at close to 93% efficiency.
>>
>>
>>Kent Osterberg
>>
>>Blue Mountain Solar. Inc.
>>
>>
>>
>>_______________________________________________ List sponsored by Home Power
>>magazine List Address: RE-wrenches at lists.re-wrenches.org Options & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out
>>participant bios: www.members.re-wrenches.org
>>_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110120/428ee543/attachment.htm>
More information about the RE-Wrenches
mailing list