[RE-wrenches] Battery Cable REvistied
William Miller
william at millersolar.com
Mon Nov 29 12:00:23 EST 2010
Ray:
I have been using a cable rated as MTW and this has been accepted by the AHJ.
William Miller
At 08:57 AM 11/29/2010, you wrote:
>HI All;
>
>I have struggled for years to get the right battery cable; in the old, old
>days we used welding cable, which was better than THHN, but not with the AHJs.
>Then we used a SAE battery cable with 532 strands that was ideal, but not
>UL listed.
>Next we used Cobra X flex, but at over 2000 strands, we had the problem it
>wasn't rated for some of the mechanical lugs and breakers. (too fine a
>stranding)
>
>Now I've found what I think is the perfect cable: Cobra Cop Flex, class I.
>http://cobrawire.com/copflex/class_i.php
>It's UL listed RHH, RHW , but is coarser stranded 532 strands, but not as
>coarse as standard THHN (19 strands).
>
>What do you guys think? RHH, RHW meets the code, with the coarser
>stranding not being a problem with regular lugs, but still way more
>flexible than THHN.
>We're saved right?
>
>
>R. Walters