<font size=3>Ray:<br><br>
I have been using a cable rated as MTW and this has been accepted by the
AHJ.<br><br>
William Miller<br><br>
<br>
At 08:57 AM 11/29/2010, you wrote:<br>
<blockquote type=cite class=cite cite>HI All;<br><br>
I have struggled for years to get the right battery cable; in the old,
old days we used welding cable, which was better than THHN, but not with
the AHJs.<br>
Then we used a SAE battery cable with 532 strands that was ideal, but not
UL listed.<br>
Next we used Cobra X flex, but at over 2000 strands, we had the problem
it wasn't rated for some of the mechanical lugs and breakers.&nbsp; (too
fine a stranding)<br><br>
Now I've found what I think is the perfect cable: Cobra Cop Flex, class
I.
<a href="http://cobrawire.com/copflex/class_i.php" eudora="autourl">http://cobrawire.com/copflex/class_i.php</a>
<br>
It's UL listed RHH, RHW , but is coarser stranded 532 strands, but not as coarse as standard THHN (19 strands).<br><br>
What do you guys think? RHH, RHW meets the code, with the coarser stranding not being a problem with regular lugs, but still way more flexible than THHN.<br>
We're saved right?<br><br>
<br>
R. Walters</font></blockquote></body>